what size wire in paralell is equal to 300 mcm and is there a reference table somwhere?
Top
Tools for Electricians:
#170491 - 11/04/07 08:57 AM Re: wire size [Re: drkana]
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
See Table 8 in Chapter 9

Roger
Top
#170515 - 11/04/07 06:29 PM Re: wire size [Re: drkana]
drkana Offline
New Member
Registered: 11/02/07
Posts: 4
Loc: illinois usa
looking at that table it looks like 3/0 or 2/0 but i'm not sure any suggestions.
Top
#170564 - 11/05/07 06:22 PM Re: wire size [Re: drkana]
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
What are you trying to do?
Don
_________________________
Don(resqcapt19)
Top
#170567 - 11/06/07 03:22 AM Re: wire size [Re: resqcapt19]
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
2/0 won't make it but, I think Don's question needs to be answered, it may save you some grief.

Roger
Top
#170615 - 11/07/07 04:30 AM Re: wire size [Re: Roger]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
With alternating current, magnetic fields build up inside the cable and skin resistance comes into play, so cable ampacity doesn't scale linearly with cross-section. In addition, cooling is related to the surface area of the cable, and larger cables have less surface area than two smaller ones to dissipate heat. Ergo, you can safely (and legally) carry more current through 2x 150MCM than through 1x 300MCM, and 2x 1/0 may be sufficient depending on what you intend.

If you're talking DC, reference Chapter 9, Table 8. If you're talking 60Hz AC, reference a combination of 310.60 with the derating rules of 310.1(B)(2)(a)... and the myraid of other codes that may apply.


Edited by SteveFehr (11/07/07 04:33 AM)
Top
#171088 - 11/19/07 11:50 AM Re: wire size [Re: SteveFehr]
earlydean Offline
Member
Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Table 310.16 takes all of this into consideration. Assuming THWN insulated copper conductors, 300 kcmil has an ampacity of 285 amps, therefore 2 paralleled 1/0 AWG conductors in separate conduit or cable would have equivalent current carrying capacity. It is necessary to keep these paralleled conductors in separate conduit or cables because of the heat buildup when more than 3 current carrying conductors are installed in one conduit (300.15(B)(2)(a))
_________________________
Earl
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
0 registered (), 79 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals