The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 61 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#170486 - 11/04/07 07:14 AM wire size
drkana Offline
New Member

Registered: 11/02/07
Posts: 4
Loc: illinois usa
what size wire in paralell is equal to 300 mcm and is there a reference table somwhere?

Top
#170491 - 11/04/07 08:57 AM Re: wire size [Re: drkana]
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
See Table 8 in Chapter 9

Roger

Top
#170515 - 11/04/07 06:29 PM Re: wire size [Re: drkana]
drkana Offline
New Member

Registered: 11/02/07
Posts: 4
Loc: illinois usa
looking at that table it looks like 3/0 or 2/0 but i'm not sure any suggestions.

Top
#170564 - 11/05/07 06:22 PM Re: wire size [Re: drkana]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
What are you trying to do?
Don
_________________________
Don(resqcapt19)

Top
#170567 - 11/06/07 03:22 AM Re: wire size [Re: resqcapt19]
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
2/0 won't make it but, I think Don's question needs to be answered, it may save you some grief.

Roger

Top
#170615 - 11/07/07 04:30 AM Re: wire size [Re: Roger]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
With alternating current, magnetic fields build up inside the cable and skin resistance comes into play, so cable ampacity doesn't scale linearly with cross-section. In addition, cooling is related to the surface area of the cable, and larger cables have less surface area than two smaller ones to dissipate heat. Ergo, you can safely (and legally) carry more current through 2x 150MCM than through 1x 300MCM, and 2x 1/0 may be sufficient depending on what you intend.

If you're talking DC, reference Chapter 9, Table 8. If you're talking 60Hz AC, reference a combination of 310.60 with the derating rules of 310.1(B)(2)(a)... and the myraid of other codes that may apply.


Edited by SteveFehr (11/07/07 04:33 AM)

Top
#171088 - 11/19/07 11:50 AM Re: wire size [Re: SteveFehr]
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Table 310.16 takes all of this into consideration. Assuming THWN insulated copper conductors, 300 kcmil has an ampacity of 285 amps, therefore 2 paralleled 1/0 AWG conductors in separate conduit or cable would have equivalent current carrying capacity. It is necessary to keep these paralleled conductors in separate conduit or cables because of the heat buildup when more than 3 current carrying conductors are installed in one conduit (300.15(B)(2)(a))
_________________________
Earl

Top