The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (LongRunner, Tjia1981), 178 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#170447 - 11/03/07 06:06 AM 210.52 Clear as Mud
rowd Offline
Member

Registered: 09/13/02
Posts: 31
Loc: Park Forest, Illinois, USA
In the illustration linked from the NEC it shows 4 feet between receptacles.The code states "Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space."

Clear as mud. once again the NEC manages to make a ruling even more muddled than it ever was to begin with.


(1) Wall Counter-top Spaces. A receptacle outlet shall be installed at each wall counter-top space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space. See related Illustration

Exception: Receptacle outlets shall not be required on a wall directly behind a range, counter-mounted cooking unit, or sink in the installation described in Figure 210.52(C)(1).

[img]http://code.necplus.org/document.php?id=necss:ill-2008:91_70hb05e210-26.gif[/img]

Top
2014 / 2011 NEC & Related Books and Study Guides
#170449 - 11/03/07 06:28 AM Re: 210.52 Clear as Mud [Re: rowd]
rowd Offline
Member

Registered: 09/13/02
Posts: 31
Loc: Park Forest, Illinois, USA
Sorry.....Here is the illustration


Top
#170450 - 11/03/07 06:55 AM Re: 210.52 Clear as Mud [Re: rowd]
JohnJ0906 Offline
Member

Registered: 10/19/06
Posts: 65
Loc: Baltimore MD USA
Exactly what is unclear?

Top
#170452 - 11/03/07 07:47 AM Re: 210.52 Clear as Mud [Re: JohnJ0906]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Seems pretty clear to me ... unless you are not sure how these things are measured.

Receptacle spacing is determined by measuring, as it were, along the baseboard (or, with counters, the backsplash). There is no allowance for the height a receptacle may be above the floor (or counter). Things that interrupt the 'usable' path (doors, sinks, ranges) are not included in the measure. If the path takes a turn, the measure follows the turn - as shown in that corner.

Legal line aside .... go buy a cheap toaster. If the cord can't reach a receptacle, you probably need to add one at that point.

Top
#170481 - 11/04/07 05:48 AM Re: 210.52 Clear as Mud [Re: renosteinke]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
I always figured that it was to make sure that there was always a receptacle within 2' of any point along the wall to go along with the standard length of appliance cords.

The 12" countertop rule probably arose because folks started putting a short piece of countertop between the stove and the end wall...and some genius ran an extention cord to it for the toaster.
_________________________
Ghost307

Top
#170495 - 11/04/07 11:41 AM Re: 210.52 Clear as Mud [Re: ghost307]
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
The key word is point. No point shall be more than 2 feet.
This same confusion occurs when receptacles in habitable rooms are to be no more than six feet from a point. The receptacles are twelve feet apart.
_________________________
Alan--
If it was easy, anyone could do it.

Top
#170514 - 11/04/07 05:50 PM Re: 210.52 Clear as Mud [Re: Alan Nadon]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
It should be noted, they say no point "along the wall line"...
It is not a radial sweep across the width of the counter.
I have heard arguments about corners.
_________________________
Greg Fretwell

Top
#170557 - 11/05/07 04:58 PM Re: 210.52 Clear as Mud [Re: gfretwell]
Jim M Offline
Member

Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
I have heard of some that did not interpret this measurement as being along the back part of the countertop and actually wanted a receptacle mounted on the 24" depth of the side wall where the countertop meet the wall.

Top
#170559 - 11/05/07 05:28 PM Re: 210.52 Clear as Mud [Re: Jim M]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You just defined the argument. It doesn't say "back" wall. ;\)
_________________________
Greg Fretwell

Top
#171777 - 12/05/07 09:45 AM Re: 210.52 Clear as Mud [Re: gfretwell]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
 Originally Posted By: gfretwell
It should be noted, they say no point "along the wall line"...
It is not a radial sweep across the width of the counter.
I have heard arguments about corners.
I think it should be changed, though, to "any point on the counter" within 2', though. What good is a rule to allow 2' cords to be used anywhere if they still can only be used butted up against the wall?

I know, I know, counters are 2' deep, and we'd need a continuous outlet for this. Really, it begs the question ... why the $&#&#$^%$^ are they only 2' cords to begin with? Why can't I get a blender with a 4' cord and a lamp with a 12' cord? Why always the rinky short cord?