#170447 - 11/03/07 06:06 AM 210.52 Clear as Mud
rowd Offline
Member
Registered: 09/13/02
Posts: 31
Loc: Park Forest, Illinois, USA
In the illustration linked from the NEC it shows 4 feet between receptacles.The code states "Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space."

Clear as mud. once again the NEC manages to make a ruling even more muddled than it ever was to begin with.


(1) Wall Counter-top Spaces. A receptacle outlet shall be installed at each wall counter-top space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space. See related Illustration

Exception: Receptacle outlets shall not be required on a wall directly behind a range, counter-mounted cooking unit, or sink in the installation described in Figure 210.52(C)(1).

Top
2017 / 2014 NEC & Related Books and Study Guides
#170449 - 11/03/07 06:28 AM Re: 210.52 Clear as Mud [Re: rowd]
rowd Offline
Member
Registered: 09/13/02
Posts: 31
Loc: Park Forest, Illinois, USA
Sorry.....Here is the illustration

Top
#170450 - 11/03/07 06:55 AM Re: 210.52 Clear as Mud [Re: rowd]
JohnJ0906 Offline
Member
Registered: 10/19/06
Posts: 65
Loc: Baltimore MD USA
Exactly what is unclear?
Top
#170452 - 11/03/07 07:47 AM Re: 210.52 Clear as Mud [Re: JohnJ0906]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Seems pretty clear to me ... unless you are not sure how these things are measured.

Receptacle spacing is determined by measuring, as it were, along the baseboard (or, with counters, the backsplash). There is no allowance for the height a receptacle may be above the floor (or counter). Things that interrupt the 'usable' path (doors, sinks, ranges) are not included in the measure. If the path takes a turn, the measure follows the turn - as shown in that corner.

Legal line aside .... go buy a cheap toaster. If the cord can't reach a receptacle, you probably need to add one at that point.
Top
#170481 - 11/04/07 05:48 AM Re: 210.52 Clear as Mud [Re: renosteinke]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
I always figured that it was to make sure that there was always a receptacle within 2' of any point along the wall to go along with the standard length of appliance cords.

The 12" countertop rule probably arose because folks started putting a short piece of countertop between the stove and the end wall...and some genius ran an extention cord to it for the toaster.
_________________________
Ghost307
Top
#170495 - 11/04/07 11:41 AM Re: 210.52 Clear as Mud [Re: ghost307]
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
The key word is point. No point shall be more than 2 feet.
This same confusion occurs when receptacles in habitable rooms are to be no more than six feet from a point. The receptacles are twelve feet apart.
_________________________
Alan--
If it was easy, anyone could do it.
Top
#170514 - 11/04/07 05:50 PM Re: 210.52 Clear as Mud [Re: Alan Nadon]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
It should be noted, they say no point "along the wall line"...
It is not a radial sweep across the width of the counter.
I have heard arguments about corners.
_________________________
Greg Fretwell
Top
#170557 - 11/05/07 04:58 PM Re: 210.52 Clear as Mud [Re: gfretwell]
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
I have heard of some that did not interpret this measurement as being along the back part of the countertop and actually wanted a receptacle mounted on the 24" depth of the side wall where the countertop meet the wall.
Top
#170559 - 11/05/07 05:28 PM Re: 210.52 Clear as Mud [Re: Jim M]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You just defined the argument. It doesn't say "back" wall. wink
_________________________
Greg Fretwell
Top
#171777 - 12/05/07 09:45 AM Re: 210.52 Clear as Mud [Re: gfretwell]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Originally Posted By gfretwell
It should be noted, they say no point "along the wall line"...
It is not a radial sweep across the width of the counter.
I have heard arguments about corners.
I think it should be changed, though, to "any point on the counter" within 2', though. What good is a rule to allow 2' cords to be used anywhere if they still can only be used butted up against the wall?

I know, I know, counters are 2' deep, and we'd need a continuous outlet for this. Really, it begs the question ... why the $&#&#$^%$^ are they only 2' cords to begin with? Why can't I get a blender with a 4' cord and a lamp with a 12' cord? Why always the rinky short cord?
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals