The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
0 registered (), 0 Guests and 172 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#170435 - 11/02/07 06:22 PM 12/4 in computer rooms
frank Offline
Member

Registered: 05/29/01
Posts: 373
Loc: windsor ontario canada
Can 12/4 be ran from three phase panels for normal and standard emergency recepticals in a computer room?
thanks

Top
2017 / 2014 NEC & Related Books and Study Guides
#170440 - 11/02/07 07:50 PM Re: 12/4 in computer rooms [Re: frank]
SP4RX Offline
Member

Registered: 10/01/07
Posts: 56
Loc: Edmonton, Alberta, Canada...eh
What exactly are "normal and standard emergency receptacles"? And I don't think I've seen any reference to computer rooms in the code book.


Shawn.

Top
#170441 - 11/02/07 08:22 PM Re: 12/4 in computer rooms [Re: SP4RX]
wacked Offline
Member

Registered: 12/19/06
Posts: 33
Are you referring to two different sources ( normal from hydro and standby, from say a UPS or a genset) inside a common piece of cable such as 12/4 bx cable?

Top
#170471 - 11/03/07 05:52 PM Re: 12/4 in computer rooms [Re: wacked]
frank Offline
Member

Registered: 05/29/01
Posts: 373
Loc: windsor ontario canada
It's a hospital so the equipment is on both generator and UPS.Would 12/4 or any 4 conductor ac90 be legal on general purpose recepticals from 3 phase panels.I have only used it for 3 phase 4 wire equipment not plugs.I'm thinking the neutral could possibly end up being to small.The 12/4 comes from the panel to a j-box where they split into circiuts.Not the way i would do it but if it passes so be it.
thanks

Top
#170517 - 11/04/07 09:06 PM Re: 12/4 in computer rooms [Re: frank]
wacked Offline
Member

Registered: 12/19/06
Posts: 33
What you have is an emergency panel feeding a UPS that feeds to outlet in a server room??? Three hots and a neutral for plugs. I don't think it is illegal as per the Canadian Electrical Code to do that unless the circuits are in a intermediate and critical care area (24-110) That said, any recent wiring I have seen done in healthcare facilities all seem to use a hot and a dedicated common labelled as such for each hot. (two wire circuits)

Top
#170536 - 11/05/07 09:31 AM Re: 12/4 in computer rooms [Re: frank]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
You can do it, but with harmonic producing loads such as that found in computer rooms, you are better off with a separate neutral for each circuit. Certain harmonics can load up the neutral beyond the ampacity of a single circuit.

Top