The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 101 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#170314 - 10/31/07 11:07 AM sizing of service conductors
stator Offline
New Member

Registered: 09/12/07
Posts: 7
Loc: va
I have an apartment complex that im installing a 1300 amp meter bank assembly (13 meter sockets, 1 main disconnect)this will be an overhead single phase 120/240 service. The point of attachment for power co. is about 20' above the meter assembly. i would amuch appreciate any help here from the board on sizing the service and grounding conductor. im currently in the process of preparing the plans for this project.

Thanks C.L


Edited by stator (10/31/07 11:15 AM)

Top
2014 / 2011 NEC & Related Books and Study Guides
#170316 - 10/31/07 12:42 PM Re: sizing of service conductors [Re: stator]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
One would need to know the size of the Service Entrance conductors to size the Grounding Electrode Conductor. When this is known use T. 250.66. You should not have to size this GEC larger than 3/0 cu or 250 KCMIL Alm. You may qualify for a smaller size based on the type of grounding electrode you find available.
Ground rods(s) Max would #6 cu, Concrete encased electrode Max #4 cu.
_________________________
George Little

Top
#170317 - 10/31/07 01:16 PM Re: sizing of service conductors [Re: George Little]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
I will go with 3/0 CU but may i ask about the service size you say 1300 amp ?? this is kinda oddball size if this was on 1200 amp service i can understand then you use the 3/0.

But for ground rod wire useally #6 will do it but becarefull here some area will required larger one typically #4 or larger

Merci, Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#170321 - 10/31/07 01:55 PM Re: sizing of service conductors [Re: frenchelectrican]
stator Offline
New Member

Registered: 09/12/07
Posts: 7
Loc: va
I stand corrected The main breaker on this will be a 1400 amp. would these service conductors be parallel?

Top
#170343 - 11/01/07 08:21 AM Re: sizing of service conductors [Re: stator]
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Unless these apartments are huge or use a lot of electricity in electric baseboard heat, 1400 amps seems way too big to me. Did you do any calculations???? 13 apartments times 100 amps each doesn't cut it. What is the total square footage? any electric ranges?, electric dryers? kitchen small appliance branch circuits? figure in demand factor per 220 part III or IV.
_________________________
Earl

Top
#170365 - 11/01/07 03:00 PM Re: sizing of service conductors [Re: earlydean]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
You might try looking at some of the examples in Annex D in the back of your code book to get an idea how to calculate the service size needed.

The calculations aren't hard. It will probably take you longer to gather the information than to do the actual calculation.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#170436 - 11/02/07 06:39 PM Re: sizing of service conductors [Re: earlydean]
stator Offline
New Member

Registered: 09/12/07
Posts: 7
Loc: va
Thanks for the reply, but its already been established what each unit is going to require, My question for the board was what size conductors are needed from point of attachment to line side of disconnect.

Top
#170437 - 11/02/07 06:57 PM Re: sizing of service conductors [Re: stator]
stator Offline
New Member

Registered: 09/12/07
Posts: 7
Loc: va
Thanks Tom, I will look Annex D over.

Top
#170439 - 11/02/07 07:46 PM Re: sizing of service conductors [Re: stator]
SP4RX Offline
Member

Registered: 10/01/07
Posts: 56
Loc: Edmonton, Alberta, Canada...eh
I couldn't agree with earlydean more: 1400 amps seems to be an extremely large service for 13 apts. Thats more than 100 amps each. Who determined that the service should be sized to 1400 amps? Are these unusually large units with air conditioning, hot tubs, and other fancy power hungry appliances? I have seen large machine shops operating lots of huge machinery with many HID lights etc. on smaller services than that.


Shawn

Top