The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Locked rotor, no burnout
by jraef
Yesterday at 01:18 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Potseal 7
Who's Online
2 registered (PoLu, eMeasure), 277 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#170261 - 10/30/07 11:57 AM Panel enclosure as raceway
bman Offline
Member

Registered: 07/07/06
Posts: 20
Loc: or
Have a job that requires "swapping" of circuits from one panel to another. Past experience tells me that one must remove said circuits entirely from panel enclosure as it is not permissible to use a panel or disconnect enclosure as a raceway for other systems. I got to looking at 300.3 4C and 312.8 and it would seem to cover panel board enclosures so long as sufficient space exists for wire fill. Thoughts?

Top
2014 / 2011 NEC & Related Books and Study Guides
#170371 - 11/01/07 05:05 PM Re: Panel enclosure as raceway [Re: bman]
bman Offline
Member

Registered: 07/07/06
Posts: 20
Loc: or
Guess its a good thing this didn’t come up on anyone’s Journeyman’s test.

Top
#170427 - 11/02/07 05:12 PM Re: Panel enclosure as raceway [Re: bman]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
408.2 says 312 applys so I;d say yer right . Long as space is there.

Top
#170456 - 11/03/07 09:26 AM Re: Panel enclosure as raceway [Re: Yoopersup]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Just be aware a lot of AHJs take the first part of that sentence seriously "Enclosures for switches or overcurrent devices shall not be used as junction boxes" and they may want you to show that the listing for that enclosure and panelboard did provide "adequate space for this purpose".
_________________________
Greg Fretwell

Top
#170546 - 11/05/07 01:11 PM Re: Panel enclosure as raceway [Re: gfretwell]
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
 Originally Posted By: gfretwell
Just be aware a lot of AHJs take the first part of that sentence seriously "Enclosures for switches or overcurrent devices shall not be used as junction boxes" and they may want you to show that the listing for that enclosure and panelboard did provide "adequate space for this purpose".


You can't just take the first part of a sentence and ignore the rest.

You are allowed to use a panel as a jbox provided you meet the rest of 312.8 and unless you are really loading up the panel with splices or it is an older smaller panel there should be plenty of room.

Top
#170561 - 11/05/07 05:50 PM Re: Panel enclosure as raceway [Re: Electricmanscott]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Scott, If I was looking at this and it was done in such a way that did not clutter up the panel too bad I wouldn't have a problem with it but I know some guys who dissagree and have a very limited interpretation of what 312.8 allows.
I have even heard more restrictive spins on this in IAEI seminars from respected road warriors.
_________________________
Greg Fretwell