Installed 2 metal halide 100 watt floodlights. You could use to wire with 220V or 110V. Pretty sure I wired right for 110 volt and had to install my own electric eyes.
Well one works fine. The other worked fine one day then would stay ON all the time. Must be a bad photcell so replaced.
But same thing. Customer saids worked one or 2 daysday then stays on.
Thanks for Any suggestions
Top
Work Gear for Electricians and the Trades
#170061 - 10/25/07 07:46 AM Re: Photocell on HID [Re: mark95]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Are you sure the start current isn't welding the contacts together?
Photocells don't tend to like switching inductive loads.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#170062 - 10/25/07 07:50 AM Re: Photocell on HID [Re: mark95]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Some of the sensors are "smart" in that you can do a secret handshake of quickly switching the power off and back on to have them stay on all the time. Thus, every time the power blinks, the lights will come on and not go out until you turn them off for a minute. Might this be the case with yours?
Top
#170065 - 10/25/07 08:59 AM Re: Photocell on HID [Re: SteveFehr]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
Make sure the photocell current rating is above the fixture current rating at the voltage you connected!. Photocells are used all the time to turn on inductive loads. Ballast's and starters.
The one in my yard (POCOS) has been working just fine for 10 years, including bulb life. Lucky I guess.

There should be a plate that slides over the eye itself. (not all models). Adjust for correct darkness, see(instructions) and make sure it is pointed in the right direction.
If there is other lighting in the area, it could be keeping your light on. Or if the eye is pointed to a dark spot, like the pole that could also keep it on.
Top
#170070 - 10/25/07 01:17 PM Re: Photocell on HID [Re: JValdes]
jdo1942 Offline
Junior Member
Registered: 11/13/05
Posts: 31
Loc: st. louis, mo. usa
Make sure your photocell is rated for ballasted lights, the ballasted rating is about 1/2 of the tungsten or incandesent rating. I believe whatever cell you are using does not have rating for metal halide.
Top
#170072 - 10/25/07 01:50 PM Re: Photocell on HID [Re: jdo1942]
wire_twister Offline
Member
Registered: 07/25/07
Posts: 265
Loc: Georgia USA
Get a Tork photocell and put it on your lights. I have installed numerous HID lights with these photocells and have not had any problems. They are a bit more expensive than some others, but you get what you pay for.













_________________________
Jimmy

Life is tough, Life is tougher when you are stupid
Top
#170095 - 10/26/07 07:17 AM Re: Photocell on HID [Re: wire_twister]
Zapped Offline
Member
Registered: 10/01/02
Posts: 482
Loc: Huntington Beach, CA, USA
I'd check your wiring and ballast draw if you've blown 2 cells in a row. Something is welding those contacts in the cell.

If this cell is a "button" type, I'd suggest using an 1800W cell, at least, for a ballasted load. They're about the same price as the 300W, and give you some extra headroom. Intermatics rarely give me problems, but I'm going to take twisters advice and take a look at the Tork products, although I've not yet installed those.

Good Luck!
Top
#170111 - 10/26/07 03:59 PM Re: Photocell on HID [Re: Zapped]
RODALCO Offline
Member
Registered: 12/08/05
Posts: 854
Loc: Titirangi, Akld, New Zealand
Check your loading !
Very likely that you weld the contacts together.
A streetlight has a very inductive load.

We only fit a photocell on a single light. Any more lights are controlled via contactors.

Cheers, Raymond
_________________________
The product of rotation, excitation and flux produces electricty.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkyinak), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals