The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
failed home inspection.
by HotLine1
17 minutes 20 seconds ago
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
2 registered (HotLine1, Webmaster), 0 Guests and 195 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#169961 - 10/21/07 06:03 PM Service Calculation
Sparky_1 Offline
Member

Registered: 11/20/04
Posts: 14
Hello,

On a residential service calculation, can the main breaker be calculated at 100% or does it have to be 80%?, code ref. please.


Top
2017 / 2014 NEC & Related Books and Study Guides
#169964 - 10/21/07 07:31 PM Re: Service Calculation [Re: Sparky_1]
Sparky_1 Offline
Member

Registered: 11/20/04
Posts: 14

The reason I ask about the main, is because I'm installing a hot tub that has dual ratings, 30 amp and 50 amp circuit. The service size is 150 Amps, with a electric range, dryer and AC for major appliances. If I do a service calculation with the added hot tub load, I get 120 amps with the 30 amp hot tub load and 132 amp with the 50 amp hot tub load, so by using the service calculations, can I put the hot tub on the 50 amp circuit or does it have to go on the 30 amp circuit?

My inspector is telling me that the calculated load can't be more than 80 % of the main breaker, 120 Amps.

I see in the code book, on page 718 example D2c that the calculated load is 144.96 with a service
size of 150 amp.

I believe that I can add to this service as long as my service calculation are 150 amp or less.


Thanks George



Edited by Sparky_1 (10/21/07 07:42 PM)

Top
#169965 - 10/21/07 07:31 PM Re: Service Calculation [Re: Sparky_1]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
And the answer is 100% The code references are: 230.42, 215.2, 210.19
The issue is "continuous load". Since residential loads are not considered to be continuous you can load a branch circit, feeder or Service to it's actual rating which is 100%. I don't think it's a good idea but the code allows it. Most inspectors would recommend a little head room and most contractors agree and provide this head room.
_________________________
George Little

Top
#169966 - 10/21/07 09:44 PM Re: Service Calculation [Re: George Little]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9063
Loc: Estero,Fl,usa
Dwelling loads better be "diverse" or we will have to repeal 310.15(B)(6) wink
_________________________
Greg Fretwell

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals