ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#169916 - 10/19/07 07:53 PM Voltage Drop and Ballasts
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
A street sign has two magnetic ballasts, 120 volts, total load of 8 amps. The run is 250 feet. When I do the math with #12 copper I get 112 volts at the load. Will low voltage affect ballast operation or ballast life?

Thanks..................B
Top
Work Gear for Electricians and the Trades
#169924 - 10/20/07 08:43 AM Re: Voltage Drop and Ballasts [Re: BigB]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
Assumming you are talking flourescent?

Provided your math is correct, (I did not calculate it), the output from the ballast will be relative to the input.
The lamps will operate sufficiently. The ballast is a XFMR. What goes in, is reflected by what goes out.
At lower voltages the lamps lose brightness. Since this is an outside application, temperature plays a major role in the brightness of the lamps.
I always recommend high output ballasts for outside use. At the lower voltage it may take some time for the lamps to achieve effective lighting. Even high output ballast's struggle in cold weather. If possible, leave the lights on 24-7.
I would run #10 copper.
Top
#169935 - 10/20/07 05:58 PM Re: Voltage Drop and Ballasts [Re: JValdes]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
120 Volts @ 8 amps and 2 ballasts sounds like 400 Watt Metal Halides to me.

Advance recommends line voltage +-10%

Top
#169942 - 10/20/07 10:31 PM Re: Voltage Drop and Ballasts [Re: electure]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
No they are fluourescent. The sign maker told me it was about 8 amps. Don't know if they're HO. I just want to get my facts right when I give him a price for #12 and a price for #10.
Top
#169946 - 10/21/07 07:58 AM Re: Voltage Drop and Ballasts [Re: BigB]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
I would use #10 for the quote and the job. This is a considerable distance.
Top
#169957 - 10/21/07 02:02 PM Re: Voltage Drop and Ballasts [Re: JValdes]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Yes I was already thinking that, the cost is not that much more. It's great to be able to get advice from everyone especially when you are just a small fish. Thanks....B
Top
#169969 - 10/22/07 08:10 AM Re: Voltage Drop and Ballasts [Re: BigB]
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
Have you considered a 12ga multi-wire branch circuit?

This would give a 3V drop if the supply is 208/120, and less than 2V if the supply is 120/240. This would be better performance than a 120V supply made with #10 conductors, and would have less total copper.

-Jon
Top
#169973 - 10/22/07 09:09 AM Re: Voltage Drop and Ballasts [Re: winnie]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
winnie....What is a "12ga multi-wire branch circuit"?
I am not sure what you mean.....John
Top
#169975 - 10/22/07 09:35 AM Re: Voltage Drop and Ballasts [Re: JValdes]
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
Sorry for being unclear.

Rather than running a 120V circuit consisting of a single ungrounded (hot) conductor and a single grounded (neutral) conductor, I am suggesting running two 120V circuits with a shared neutral, consisting of two ungrounded conductors from two different supply legs and a single grounded conductor. This is called a multi-wire branch circuit (MWBC), the benefits and issues of which are regularly debated. I am not saying that this _is_ the best circuit to use in this case, simply suggesting that it be considered.

In the ideal 'balanced' case, no current flows on the neutral, so that there is no voltage drop on the neutral. In the case of two legs from a three phase system, or in the case of harmonics, there will be voltage drop on the neutral, but it will be reduced from the single circuit case.

Rather than 8A on a single circuit, you have 4A on each of two circuits.

The net result is that the length of conductor over which you consider voltage drop is reduced, and the current flow causing the voltage drop is reduced. The benefit of the MWBC is so large in this case that the voltage drop is lower if you use 12ga conductors in this configuration than if you use 10ga conductors in a single circuit configuration.

4 #12 conductors contain less total copper than 3 #10 conductors. (Remember the EGC!) So the wire is probably less expensive even though you have more conductors.

The cost adder is that you need a double pole breaker, and double pole switches.

-Jon
Top
#169997 - 10/23/07 07:50 AM Re: Voltage Drop and Ballasts [Re: winnie]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
Thanks for the clarification winnie. Never would have crossed my mind. I learn something everyday. Thanks John
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals