The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 18
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 254 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#169841 - 10/17/07 06:17 PM Gfi's and testers.
derater Offline
Member

Registered: 03/30/02
Posts: 182
Could use some insight on this; gfi receptacle trips with 'test' button, but not with a gfi tester. New type that supposedly won't work if wired wrong. Tester is ok. Ideas ?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#169843 - 10/17/07 06:29 PM Re: Gfi's and testers. [Re: derater]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
No ground?
_________________________
Greg Fretwell

Top
#169846 - 10/17/07 07:32 PM Re: Gfi's and testers. [Re: gfretwell]
SP4RX Offline
Member

Registered: 10/01/07
Posts: 56
Loc: Edmonton, Alberta, Canada...eh
I agree with Fretwell. I think that the gfi tester works by allowing a small amount of current to flow from the hot conductor through a resistor to the grounding conductor. So if you have no ground connection at the gfi the tester's ground prong wouldn't have a good return path for the simulated ground fault.
This doesn't mean that the gfi won't work as intended though since it normally compares line current to neutral current, with no need for a ground.
Perhaps you could verify it's correct operation by unscrewing the gfi and, using a separate wire, make a temporary connection to a good remote ground point and then try your tester again?

Shawn.

Top
#169858 - 10/18/07 09:54 AM Re: Gfi's and testers. [Re: SP4RX]
JValdes Offline
Member

Registered: 06/03/07
Posts: 308
Loc: South Carolina
The neutral carries the same current as the hot conductor. A ground would be necessary for the GFCI to work properly.

Top
#169859 - 10/18/07 10:12 AM Re: Gfi's and testers. [Re: JValdes]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
 Originally Posted By: JValdes
The neutral carries the same current as the hot conductor. A ground would be necessary for the GFCI to work properly.
The GFCI will still work properly without a ground (hence its acceptability in ungrounded retrofit appliations) but the GFCI tester wouldn't work, as it can't shunt a small amount of current to ground if there's no ground to shunt to. Standing in a puddle and sticking a wet finger into the receptacle aught to do the trick, though. But it's certainly not recommend as the consequences if the test fails are potentially rather dire...


Edited by SteveFehr (10/18/07 10:13 AM)

Top
#169865 - 10/18/07 12:56 PM Re: Gfi's and testers. [Re: SteveFehr]
derater Offline
Member

Registered: 03/30/02
Posts: 182
Thanks all. That's the case, no ground.

Top