#169841 - 10/17/07 06:17 PM Gfi's and testers.
derater Offline
Member
Registered: 03/30/02
Posts: 179
Could use some insight on this; gfi receptacle trips with 'test' button, but not with a gfi tester. New type that supposedly won't work if wired wrong. Tester is ok. Ideas ?
Top
Work Gear for Electricians and the Trades
#169843 - 10/17/07 06:29 PM Re: Gfi's and testers. [Re: derater]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
No ground?
_________________________
Greg Fretwell
Top
#169846 - 10/17/07 07:32 PM Re: Gfi's and testers. [Re: gfretwell]
SP4RX Offline
Member
Registered: 10/01/07
Posts: 56
Loc: Edmonton, Alberta, Canada...eh
I agree with Fretwell. I think that the gfi tester works by allowing a small amount of current to flow from the hot conductor through a resistor to the grounding conductor. So if you have no ground connection at the gfi the tester's ground prong wouldn't have a good return path for the simulated ground fault.
This doesn't mean that the gfi won't work as intended though since it normally compares line current to neutral current, with no need for a ground.
Perhaps you could verify it's correct operation by unscrewing the gfi and, using a separate wire, make a temporary connection to a good remote ground point and then try your tester again?

Shawn.
Top
#169858 - 10/18/07 09:54 AM Re: Gfi's and testers. [Re: SP4RX]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
The neutral carries the same current as the hot conductor. A ground would be necessary for the GFCI to work properly.
Top
#169859 - 10/18/07 10:12 AM Re: Gfi's and testers. [Re: JValdes]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Originally Posted By JValdes
The neutral carries the same current as the hot conductor. A ground would be necessary for the GFCI to work properly.
The GFCI will still work properly without a ground (hence its acceptability in ungrounded retrofit appliations) but the GFCI tester wouldn't work, as it can't shunt a small amount of current to ground if there's no ground to shunt to. Standing in a puddle and sticking a wet finger into the receptacle aught to do the trick, though. But it's certainly not recommend as the consequences if the test fails are potentially rather dire...


Edited by SteveFehr (10/18/07 10:13 AM)
Top
#169865 - 10/18/07 12:56 PM Re: Gfi's and testers. [Re: SteveFehr]
derater Offline
Member
Registered: 03/30/02
Posts: 179
Thanks all. That's the case, no ground.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals