#169836 - 10/17/07 04:26 PM Hospital Grade Cap
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
If we have a piece of medical equipment with a "Hospital Grade" cap on the cord must it be provided with a "Hospital Grade" receptacle?
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#169837 - 10/17/07 04:52 PM Re: Hospital Grade Cap [Re: George Little]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Nope.

If a location required everything to be 'hospital grade,' then both cap and recep would need to meet the requirements. However, there is nothing that forbids placing the appliance in other locations.

"Hospital grade" simply means that the devices meet tougher criteria. Indeed, the practice of sever manufacturers is to simply pull product off their regular production line, and stamp those specific pieces that meet the higher standards. In terms of ordinary use, the components are perfectly interchangeable.
Top
#169839 - 10/17/07 04:55 PM Re: Hospital Grade Cap [Re: George Little]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
Listing and Labeling of the equipment with the plug prehaps?? Might be worth a look to see if Equipment requires it??
Top
#169857 - 10/18/07 09:53 AM Re: Hospital Grade Cap [Re: Yoopersup]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Hospital grade means they have to conform to certain hospital UL standards and are built better than the average cheap plug, but they still conform to NEMA 5-15 and all applicable standard UL listings for plugs. It's perfectly acceptable to plug a hospital plug into a non-hospital receptacle.

http://www.interpower.com/ic/medical_info.asp
Top
#169866 - 10/18/07 01:17 PM Re: Hospital Grade Cap [Re: SteveFehr]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Steve- Based on your reference to "interpower" (which was excellent) I feel that it would be reasonable to look for a hospital grade receptacle when inspecting the job since the grounding is the whole reason for installing the hospital grade cap on the cord. The hospital grade receptacle would provide similar standards and be compatible with the cap. Am I in left field?
_________________________
George Little
Top
#169868 - 10/18/07 02:34 PM Re: Hospital Grade Cap [Re: George Little]
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
George, actually providing the equipment with a HG cord cap just means it is acceptable for use at a Patient Bed.

Even though most of this equipment has some mention of "Superior Grounding" being an issue, it really has no bearing on an HG receptacle being required.

If the equipment is used outside a Patient Care Area, the redundant grounding required by 517.13 is not present anyways.

Roger

Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
0 registered (), 79 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals