The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
1 registered (gfretwell), 316 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#169836 - 10/17/07 04:26 PM Hospital Grade Cap
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
If we have a piece of medical equipment with a "Hospital Grade" cap on the cord must it be provided with a "Hospital Grade" receptacle?
George Little

2014 / 2011 NEC & Related Books and Study Guides
#169837 - 10/17/07 04:52 PM Re: Hospital Grade Cap [Re: George Little]
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country

If a location required everything to be 'hospital grade,' then both cap and recep would need to meet the requirements. However, there is nothing that forbids placing the appliance in other locations.

"Hospital grade" simply means that the devices meet tougher criteria. Indeed, the practice of sever manufacturers is to simply pull product off their regular production line, and stamp those specific pieces that meet the higher standards. In terms of ordinary use, the components are perfectly interchangeable.

#169839 - 10/17/07 04:55 PM Re: Hospital Grade Cap [Re: George Little]
Yoopersup Offline

Registered: 03/04/03
Posts: 826
Loc: Michigan
Listing and Labeling of the equipment with the plug prehaps?? Might be worth a look to see if Equipment requires it??

#169857 - 10/18/07 09:53 AM Re: Hospital Grade Cap [Re: Yoopersup]
SteveFehr Offline

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Hospital grade means they have to conform to certain hospital UL standards and are built better than the average cheap plug, but they still conform to NEMA 5-15 and all applicable standard UL listings for plugs. It's perfectly acceptable to plug a hospital plug into a non-hospital receptacle.

#169866 - 10/18/07 01:17 PM Re: Hospital Grade Cap [Re: SteveFehr]
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Steve- Based on your reference to "interpower" (which was excellent) I feel that it would be reasonable to look for a hospital grade receptacle when inspecting the job since the grounding is the whole reason for installing the hospital grade cap on the cord. The hospital grade receptacle would provide similar standards and be compatible with the cap. Am I in left field?
George Little

#169868 - 10/18/07 02:34 PM Re: Hospital Grade Cap [Re: George Little]
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
George, actually providing the equipment with a HG cord cap just means it is acceptable for use at a Patient Bed.

Even though most of this equipment has some mention of "Superior Grounding" being an issue, it really has no bearing on an HG receptacle being required.

If the equipment is used outside a Patient Care Area, the redundant grounding required by 517.13 is not present anyways.