The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Yesterday at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 9
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 8 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#169658 - 10/11/07 12:19 AM Motor disconnecting means
ih17dka8 Offline
Junior Member

Registered: 01/16/06
Posts: 8
Loc: Seoul, South Korea
Only if within sight of motor, using branch circuit breaker(a dedicated circuit breaker in panelboard for motor) as a disconnecting means is enough without additional safety switch regardless of motor horsepower for NEC code. Is that right?

NEC 430.109(A) shows that "molded case circuit breaker" can be served as a disconnecting means for motor.

However NEC 430.109(B)describe that "For stationary motors of 1⁄8 hp or less, the branch-circuit overcurrent shall be permitted to serve as the disconnecting means.

Would you enlighten me with your opinion?

Top
2014 / 2011 NEC & Related Books and Study Guides
#169666 - 10/11/07 07:04 AM Re: Motor disconnecting means [Re: ih17dka8]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1297
Loc: Alaska
1/8 hp max if using a breaker. 430.109(A) is general conditions while(B) is specific. When I get confused on an article, I will read the entire article. Then I will "remove" all the paragraphs that do not apply to my situation then read it again. In this case if you only read 430.109,430.109(A), and 430.109(B), you ought to be enlightened.