The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#169658 - 10/11/07 12:19 AM Motor disconnecting means
ih17dka8 Offline
Junior Member

Registered: 01/16/06
Posts: 8
Loc: Seoul, South Korea
Only if within sight of motor, using branch circuit breaker(a dedicated circuit breaker in panelboard for motor) as a disconnecting means is enough without additional safety switch regardless of motor horsepower for NEC code. Is that right?

NEC 430.109(A) shows that "molded case circuit breaker" can be served as a disconnecting means for motor.

However NEC 430.109(B)describe that "For stationary motors of 1⁄8 hp or less, the branch-circuit overcurrent shall be permitted to serve as the disconnecting means.

Would you enlighten me with your opinion?

2014 / 2011 NEC & Related Books and Study Guides
#169666 - 10/11/07 07:04 AM Re: Motor disconnecting means [Re: ih17dka8]
sparkyinak Offline

Registered: 07/08/07
Posts: 1288
Loc: Alaska
1/8 hp max if using a breaker. 430.109(A) is general conditions while(B) is specific. When I get confused on an article, I will read the entire article. Then I will "remove" all the paragraphs that do not apply to my situation then read it again. In this case if you only read 430.109,430.109(A), and 430.109(B), you ought to be enlightened.