The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Massive power outage South Australia
by Meadow
Today at 06:46 AM
short circuit??
by Meadow
Today at 06:43 AM
Norwegian power?
by Meadow
Today at 06:36 AM
breaker meltdown
by sparky
09/27/16 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 83 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#169357 - 10/02/07 08:26 PM Line Loss Question
bwise121 Offline
Member

Registered: 09/11/03
Posts: 113
Loc: Sacramento, CA USA
I have to feed a subpanel for an underground well. It is 250' from the panel and I have calculated with 27.5A 240V load, I'll need to run a #6 feeder. Here is the problem. The contractor installing the well and pump told me that the actual pump will be 200' underground. So, he is going to have a cord all the way down to the bottom and that is where the motor will be. Do I need to calculate this into the line loss? So a total length of 450'??

Please advise.

Thanks,
Byron

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#169358 - 10/02/07 10:29 PM Re: Line Loss Question [Re: bwise121]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
5 HP pump?
_________________________
Greg Fretwell

Top
#169359 - 10/02/07 10:47 PM Re: Line Loss Question [Re: gfretwell]
bwise121 Offline
Member

Registered: 09/11/03
Posts: 113
Loc: Sacramento, CA USA
I was only told the amps and the voltage but that sounds right.

Top
#169360 - 10/02/07 11:03 PM Re: Line Loss Question [Re: bwise121]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
you say one run at 250 feet then add 200 more feet down the well if so the total run is 450 feet

my main condseration you will run some issue with voltage drop with this length of wire here

i came up the caluation it will reqired # 3 yeah #3 copper wire for full run with the vd of 6.2 volt drop or 2.6 % vd but with your figures i will post it here

with your figures with #6 wires it will have 5.2% VD or 12.4 volt drop

all the figures are based on 240 volt supply and useing the THHN/THWN wires for other type wires it can change the figures all the figures are based on 75°C termation rating

and i think you are very right on borderline with the VD

Merci, Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#169361 - 10/02/07 11:26 PM Re: Line Loss Question [Re: frenchelectrican]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
How about a buck&boost transformer by the subpanel? instead of the large copper wire.
_________________________
Be kind to your neighbor, he knows where you live


Top
#169366 - 10/03/07 03:58 AM Re: Line Loss Question [Re: Niko]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
What voltage is the pump rated for? 3% & 5% voltage drop is not an NEC requirement, merely a recommendation for a quality installation so that people get enough voltage at the furthest outlet under all conditions. As this circuit is only running a pump, you only need to worry about the pump and not "what if they plug THIS in?"- can it take 208V? If so, you only really need to calculate cable size to support 208V at 27.5A, and 10% (or even 12%) drop is OK, though you need to have some leeway should the 240V drop a few volts at the panel due to voltage drop in the service feeder, etc.

IF the pump is rated for 208V, #10 (12.4% drop to 210V) would be acceptable for this circuit, but I'd probably run #8 to be safe (7.8% drop to 221V). Otherwise, if it's rated for 220 or 230, etc, just make sure you're meeting the required voltage.

Electric bills are also a concern; the smaller the cable, the higher the resistance, the more energy will be wasted as lost heat, as much as 820W in the case of the #10 feed I outlined. If this pump runs 4 hours a day, that's about $72/year at 0.06/kwh, and more if you're in CA or somewhere with expensive electricity. So, larger cable could easily be cost-justified for that alone.


Edited by SteveFehr (10/03/07 04:03 AM)

Top
#169372 - 10/03/07 07:13 AM Re: Line Loss Question [Re: SteveFehr]
sabrown Offline
Member

Registered: 12/12/02
Posts: 297
Loc: Ogden, Utah, USA
The other place to look is typical info from the pump manufacturer. As many pumps use Franklin Electric motors, taking from the "Aplication-Installation-Maintainance" manual, assuming that 5hp, 1-phase, and 240 VAC is correct, then for 450' from the service entrance to the motor they recommend #6 AWG minimum. This is for 5% Vd, for 3% a #4 is close but you would need to go to a #3 AWG.

The 27.5a would be maximum service factor load for "FE's" 5hp. The pump is rated for 3.7 KW and >0.97 power factor running.

I highly recommend getting the pumps data and verifying these numbers versus taking a wild guess on to little data.

Shane


Edited by sabrown (10/03/07 07:15 AM)
Edit Reason: Added voltage drop info.

Top
#169511 - 10/06/07 02:10 PM Re: Line Loss Question [Re: sabrown]
PE&Master Offline
Member

Registered: 02/25/06
Posts: 138
Loc: TX, USA
You'll need to look at this as a two headed problem, the drop from the service to the pump house and the drop from the pump house to the pump.

I'll assume the pump guy is providing the wiring and connection from the the ground down to the pump. He has a cable his plans to use. Figure the voltage drop for that part.

To keep within the recommend 5% drop, see what wire size you'll need to have for the feeder you're providing.

Running a pump on lower than designed voltage will cause it to run hotter and thus fail quicker.

Top
#169568 - 10/08/07 11:43 AM Re: Line Loss Question [Re: PE&Master]
Ann Brush Offline
Member

Registered: 12/27/05
Posts: 155
Loc: Ohia
We have a similar installation at a research unit - 450 feet to the well and then 276 feet down. Original installer used #10 copper - the cost to retrench with new wire etc was prohibitive. In the end we stuck a variable speed pump down the well with some sort of a controller panel at the breaker - it was way less expensive.

Top
#169686 - 10/11/07 07:27 PM Re: Line Loss Question [Re: Ann Brush]
bwise121 Offline
Member

Registered: 09/11/03
Posts: 113
Loc: Sacramento, CA USA
I've pressed the owner/well installer for more info particularly if the motor will run at 208V. The well installer insists that #6 will suffice however I'm questioning the effectiveness of the motor with that line loss.

As a contingency plan I do like the Buck & Boost transformer option. Assuming the voltage is around 208 by the time it gets to the panel, and the motor takes 240V which transformer is the best choice? Also, can someone explain the Power Rating and what it means.

Thanks,
Byron