The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
0 registered (), 0 Guests and 63 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#169317 - 10/01/07 03:25 PM 480v parking lot lighting
etech Offline
Member

Registered: 06/16/07
Posts: 17
Loc: Oregon
We reto-fitted parking lot lighting from 208v to 480v, one ckt. keeps shorting out. Wire is rated for 600v. Lights work for two months at a time. Any feed back will be welcomed.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#169318 - 10/01/07 03:55 PM Re: 480v parking lot lighting [Re: etech]
frenchelectrican Offline


Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
what the oringail luminaire wired on 120 v or 208 volt??

and i will suggest to megger the line to find out sometime you will get a bad spot of wire.

rule of thumb anytime you increase the voltage on parking lot luminaire system is megger it first if the wire are fine otherwise replace it.

that useally take care of bad curpits with connection and who know what happend in the pipe as well

what the wattage on the luminaires now ?? and the voltage it is on now 277 or 480 ??

if the megger pass the test then you should amprobe it to check the current drawage make sure it dont get too much loading escpally with the MWBC set up

Merci , Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#169322 - 10/01/07 06:49 PM Re: 480v parking lot lighting [Re: frenchelectrican]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Such problems can be quite vexing.

What I ended up doing in a similar situation was to put in-line fuses on BOTH wires, at the base of the fixture. I was then able to identify the fixtures that were giving us trouble.

Top
#169330 - 10/01/07 08:56 PM Re: 480v parking lot lighting [Re: renosteinke]
RODALCO Offline
Member

Registered: 12/08/05
Posts: 865
Loc: Titirangi, Akld, New Zealand
As already said by frenchelectrician, sectionalise and megger all cables concerned and check the insulation resistance between cables to lamps.
Hopefully you don't have breach joints in the SL circuits.
These usually get damp because of poor sealing of the outer sleeving.
The increased voltage will cause them to break down faster and hence intermittand faults once in a while.

From control point lightcell contactor, fit section fuses on each outgoing SL circuit.

Also check the overall loading per string of lights.

Fit fuses in each lamp acces cover if not already there.
_________________________
The product of rotation, excitation and flux produces electricty.

Top
#169352 - 10/02/07 04:50 PM Re: 480v parking lot lighting [Re: RODALCO]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1308
Loc: Alaska
I would account for all the runs of wires in case the origional circuit picked up an remote outlet or some other light like a lighted sign or something. Being that the voltage was boosted, if anything was left on circuit, it is safe to say it's toast. Eliminate the easy things first before megging the wires or adding fuses. Do you recall the weather conditions a few days before the outage(s)?
_________________________
"Live Awesome!" - Kevin Carosa