I was asked if a 120v. 15a. circuit to a furnace located in a bedroom needs AFCI protection and if I'm not mistaken the answer would be yes. What say you?
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#169118 - 09/25/07 05:36 PM Re: AFCI on a furnace [Re: George Little]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
George .... I'd love to hear how this application turns out.

As written the furnace would need an AFCI. Nor does the new version allow any exceptions for appliances that use igniters for the gas flame, rather than having a pilot light.

When an igniter operates, that sure looks like a spark to me. Either the AFCI will shut down the appliance .... or I am completely misled as to just what an AFCI is supposed to do!
Top
#169120 - 09/25/07 05:40 PM Re: AFCI on a furnace [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
If you gotta put the smokes on AFCI, I sure don't see any relief for anything else. The only question would be if it was really "in" the bedroom. (the old "closet" question)
_________________________
Greg Fretwell
Top
#169121 - 09/25/07 05:44 PM Re: AFCI on a furnace [Re: gfretwell]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Thanks Greg I agree. As for clarification the furnace is a horizontal furnace located above the closet and is serviced standing on a ladder located in the bedroom. I would say it is in the bedroom.
_________________________
George Little
Top
#169122 - 09/25/07 05:48 PM Re: AFCI on a furnace [Re: George Little]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Reno- I don't think the spark ignition would trip the AFCI because it's supplied by a xformer but I could be wrong. The AFCI only sees arc's on the 120v. lines.???
_________________________
George Little
Top
#169127 - 09/25/07 08:18 PM Re: AFCI on a furnace [Re: George Little]
ArkySparky2B Offline
Junior Member
Registered: 03/21/07
Posts: 6
Loc: Jonesboro Arkansas
Is this furnace open to the room, or is it in an enclosed area, with just an access panel? If it is in an enclosed area, I would consider it technically not in the "bedroom".
Plus, as a HVAC tech, the last thing I would want to see is the furnace on an arc fault. The risk of the arc fault tripping out is too great, leaving the home without heat when it is needed the most.
_________________________
It's all about herding those electrons.
Top
#169128 - 09/25/07 10:23 PM Re: AFCI on a furnace [Re: ArkySparky2B]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
George, I agree this should not be tripping the AFCI. The AFCI is really looking for a series of short, high current events. (on the order of 50a or more). I can't see an igniter doing anything like that.
_________________________
Greg Fretwell
Top
#169129 - 09/26/07 02:37 AM Re: AFCI on a furnace [Re: gfretwell]
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
If the AFCI does trip due to the igniter IMO it will be the GFP portion of a AFCI that is causing the trip. (All AFCIs have built GFP protection in the 30 ma range if I recall)

I also with Greg's point about the transformer providing some isolation.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#169132 - 09/26/07 04:54 AM Re: AFCI on a furnace [Re: iwire]
Elec N Spec Offline
Member
Registered: 07/06/06
Posts: 33
Loc: Rochester Hills, MI USA
My vote would be that it had to be AFCI protected. I agree that if a smoke alarm has to be protected a furnace should be protected as well.

Tony T.
Top
#169135 - 09/26/07 06:53 AM Re: AFCI on a furnace [Re: Elec N Spec]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Iwire, I'm no expert on AFCI design however why do you thing the GFCI side of the AFCI would trip? If it is working properly, the GFCI portions measues power in/power out. If there is a difference of a few millivolts, it trips. If the igniter is grounding out then yes it would trip.


Edited by sparkyinak (09/26/07 06:54 AM)
Edit Reason: Do not know how to spell AFCI
_________________________
"Live Awesome!" - Kevin Carosa
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 64 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals