The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 101 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#168349 - 09/01/07 07:28 PM Got hit by a HI POT
Clydesdale Offline
Member

Registered: 11/25/04
Posts: 139
A couple of months ago, I had the displeasure of being assinged to put together some modular "boxes" at a modular home factory. I was there for a few weeks, and let me say that I can't believe what I saw. They notch the studs, and use nail plates everywhere. A lot of the sheetrock goes up BEFORE they box out the units, and are nailed on from behind. Anyway I digress.

I was plugging and swiching on one of the finish staged boxes, and every trade(if you want to call them that) is around you with nail guns, saws, drills, paint rollers...LOTS OF NOISE. You can't hear much. So one of my fellow "electricians" casually says very low...."hey, we're doing the HI POT." Well, needless to say, I didn't here him, or he didn't make sure I heard him...whatever the case, as I was holding a grounded switch in my left hand and was wrapping the feed around the screw terminalwith my right hand, pressing pretty hard with my right thumb to get the wire just right before I squeeze the wire hook with my strippers, something I can only compare to "hands the size of God's" shook me once, and only because I let go pretty quick. I stood there for a moment and thought, "that was more than 110V."

Then another first happened.....I started to smell a buring smell...like hair or flesh....from within my body. Very strage...anyway, thank god I never have to go back to that place. I can't beleive some of the guys have been there for over 14 years. Pretty crazy. I took a reading of what hit me afterwards, and it was over 900V.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#168368 - 09/02/07 09:30 AM Re: Got hit by a HI POT [Re: Clydesdale]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Sounds like a good place to be rid of. Those reckless, immature SOB's thought it would be funny to 'zap' the new guy. What they need is a manager with balls enough to see to their immediate termination.

You didn't let go 'fast enough.' You let go because the tester let you let go. Absent the designed-in limits to the test equipment, you would be posting from St. Peters' internet connection.

Horseplay has no place in the workplace. Sure, we all like a good chuckle from time to time ... that's why we tell 'blonde' jokes \:D It's one thing to ask the new supply clerk for a can of motor smoke ... quite another to zap someone.

Not only need you be able to communicate with your co-workers ... you are trusting each other with your lives. Period. If a man isn't mature enough to handle that responsibility, I don't want him on my jobsite. Period.

Top
#168373 - 09/02/07 10:34 AM Re: Got hit by a HI POT [Re: renosteinke]
steve ancient apprentice Offline
Member

Registered: 03/04/05
Posts: 170
Loc: west springfield,mass
Reno hit this right on the head. I havve seen many accidents and by intentionally zapping some one is a total disregaurd for someones life. If they were doing a test then everyone should have benn made aware of this and to make sure there was no way anyone could be shocked. I find no humor in this and a test of this should have been done after everyone was made aware of the test and not before.There would havve been heck (not what i wanted to say) to pay if this happened to me. When im working with someone no booze during work, NO HORSEPAY. Plenty of time later to do that.
Always,
Steve

Top
#168377 - 09/02/07 03:15 PM Re: Got hit by a HI POT [Re: Clydesdale]
togol Offline
Member

Registered: 09/15/05
Posts: 426
Loc: NW In. USA
probably should have called OHSA, the cops........then a lawyer...twenty years from now you'll be glad you did
_________________________
Tom

Top
#168388 - 09/03/07 01:28 AM Re: Got hit by a HI POT [Re: togol]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
OK,
Since when has a High Potential test been in the vicinity of 900V?.
All of the High Potential tests that I've been involved with have been 5000V+.
I think you are confusing a Megger test with a Hi-Pot Test.
Meg-ohm meters use twice the AC RMS voltage as a DC voltage.
For 120VAC this would be 250VDC, for 240VAC this would be 500VDC.
For 400V here in NZ it would be 1000VDC.
Now, I work for a PoCo, company rules state that you MUST be wearing Rubber Gloves and outers before the test starts.
You NEVER muck with HV stuff.
One of our store-men used to be a Line Mechanic, he is missing some of his face and has one finger and a thumb on one hand and two fingers on the other hand.
Cable blew up on a High Potential Test, we get everyone out of the way when we do these tests these days, it was nasty that day. \:\(


Edited by Trumpy (09/03/07 02:16 AM)
Edit Reason: Edit voltages
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#168396 - 09/03/07 07:22 AM Re: Got hit by a HI POT [Re: Trumpy]
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
 Originally Posted By: Trumpy
For 400V here in NZ it would be 1000VDC.


Interesting -- BS7671 here only requires 500V DC megger tests for both 240V single phase and 415V 3-phase. Most electronic meggers do have a 1000V range though.

Top
#168402 - 09/03/07 09:43 AM Re: Got hit by a HI POT [Re: Trumpy]
togol Offline
Member

Registered: 09/15/05
Posts: 426
Loc: NW In. USA
Mike, I had the same thought about the Megger after I had replied. seemed very low for a Hi-Pot test which is kinda overboard for resi wiring IMO / or Clydesdale is one really lucky guy
_________________________
Tom

Top
#168404 - 09/03/07 11:15 AM Re: Got hit by a HI POT [Re: togol]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Mike, Tom .... whatever the specific equipment used, it comes back to two things:
1) Clydesdale was spared serious harm by the limitations of the equipment; and,
2) The test was carried out in an almost criminally negligent manner.


Edited by renosteinke (09/03/07 11:15 AM)

Top
#168433 - 09/04/07 02:06 PM Re: Got hit by a HI POT [Re: renosteinke]
dilydalyer Offline
Member

Registered: 01/08/07
Posts: 59
Loc: tennessee
Glad ur ok....I mean SORTA ok:{

Top
#168471 - 09/05/07 04:49 PM Re: Got hit by a HI POT [Re: renosteinke]
togol Offline
Member

Registered: 09/15/05
Posts: 426
Loc: NW In. USA
John I couldn't agree more, and I wasn't trying to diminish what happened to Clydesdale at all


I was just wondering why that redneck" co-worker " said he was hi-potting house wiring.