#168264 - 08/30/07 10:07 AM Hieght of main disconnect?
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
What is the maximum ht of a main disconnect and where is it in the code?
Top
2017 / 2014 NEC & Related Books and Study Guides
#168269 - 08/30/07 04:32 PM Re: Hieght of main disconnect? [Re: cgw]
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
6' 7" to the center of the grip when in its highest position. 404.8(A)
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#168548 - 09/08/07 08:38 AM Re: Hieght of main disconnect? [Re: Tom]
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
How about a meter?

Deck extends out 5', 4' high (bottom of the joists), 2" out the top thru the deck floor to the WH.
No lattice or other obstructions.

(NH) would this be a utility call or AHJ,Code etc.?

Not done, but the question was raised by the home owner.
We're in the building stage now. wrap around deck, No need for it, but the HO wants the extra 3' of deck.
Top
#168549 - 09/08/07 09:02 AM Re: Hieght of main disconnect? [Re: leland]
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
Many AHJ and utilities consider the meter as electrical equipment subject to 110.26 Clear work space.
The utility will be the ultimate judge of location for a meter and may require it to be moved.
When people come in for their building permit for a deck the first question we ask is where the gas and electric are located. Firemen do not like to climb under a deck to shut off gas and electric when there is a fire.
_________________________
Alan--
If it was easy, anyone could do it.
Top
#168551 - 09/08/07 09:32 AM Re: Hieght of main disconnect? [Re: Alan Nadon]
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
Thanx, My advice was against it, I figured the work space.
But with enquireing minds I don't want to give a bad answer and have them get the info and think I gave a line of "stuff".
Top
#168559 - 09/08/07 06:52 PM Re: Hieght of main disconnect? [Re: leland]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Consider the language of 110.26 "likely to require examination, adjustment, servicing, or maintenance while energized".
I think service equipment should always qualify.
They are not going to drop the primary fuse on the transformer if they open the meter can.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals