The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
gfretwell 11
sparkyinak 10
ghost307 10
Trumpy 8
Who's Online
0 registered (), 266 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#167751 - 08/19/07 12:26 PM Circuit Design
windmiller Offline
Junior Member

Registered: 12/05/06
Posts: 43
Loc: Alaska
Whats the rule on feeding a 300A Fused Disconect from a 400A breaker?

thanks

Windmiller
_________________________
We all live under one King

Top
2014 / 2011 NEC & Related Books and Study Guides
#167759 - 08/19/07 05:05 PM Re: Circuit Design [Re: windmiller]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6824
Loc: Brick, NJ USA
More info required for answer.
_________________________
John

Top
#167768 - 08/19/07 07:39 PM Re: Circuit Design [Re: HotLine1]
windmiller Offline
Junior Member

Registered: 12/05/06
Posts: 43
Loc: Alaska
Hi,
This is from a 480 V MCC to a maint. shop.

This is a feeder to supply power to the building.

No 300A plug in bucket is available and no other place to get power except from 480V MCC with a new section and a frame mounted 400 CB.

The feeder is 3/C 500 MC.

Thanks,

Windmiller
_________________________
We all live under one King

Top
#167770 - 08/19/07 07:56 PM Re: Circuit Design [Re: windmiller]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9058
Loc: Estero,Fl,usa
500 MCM is 380a @ 75c
I don't see a real problem. If you can get in under the feeder tap rules it is a slam dunk and you can probably use 240.4(B) if it comes down to it.

From a practical sense, you are really only providing short circuit protection in the 400a breaker since overload protection will come with the 300a. That is how they rationalize the "tap rules".


Edited by gfretwell (08/19/07 07:57 PM)
_________________________
Greg Fretwell

Top
#167907 - 08/22/07 11:36 AM Re: Circuit Design [Re: windmiller]
electure Offline


Member

Registered: 12/24/00
Posts: 4227
Loc: Fullerton, CA USA
 Quote:
This is a feeder to supply power to the building.


If so, it may qualify for an outside the building tap of unlimited length per 240.21(B)(5)