The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 193 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#167721 - 08/18/07 02:42 PM 13.8 kV Cable Installation
windmiller Offline
Junior Member

Registered: 12/05/06
Posts: 43
Loc: Alaska
Is it permissable to install a 13.8 kV MC cable on the ground or does the cable have to be buried per 300.50 or does 300.37 allow this with MC cable?

Thank you,


Edited by windmiller (08/18/07 02:45 PM)
Edit Reason: additional info
We all live under one King

2014 / 2011 NEC & Related Books and Study Guides
#167734 - 08/18/07 07:28 PM Re: 13.8 kV Cable Installation [Re: windmiller]
Yoopersup Offline

Registered: 03/04/03
Posts: 826
Loc: Michigan
328.10 & 328.12 Medium Voltage Cable

330.10b(4)MC uses primitted

300.37Requirements for over 600 Volts ,Nominal

Definitions read Exposed (as refered to un 300.37

My opinion No(must be underground or in a raceway or support system (tray) above ground. if subject to physical harm . Or Exposed to unqualified persons.