The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
56 minutes 30 seconds ago
Looking for older post
by Trumpy
Today at 01:04 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
Webmaster > Admin
by Trumpy
Yesterday at 08:29 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
1 registered (geoff in UK), 150 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#167721 - 08/18/07 02:42 PM 13.8 kV Cable Installation
windmiller Offline
Junior Member

Registered: 12/05/06
Posts: 43
Loc: Alaska
Is it permissable to install a 13.8 kV MC cable on the ground or does the cable have to be buried per 300.50 or does 300.37 allow this with MC cable?

Thank you,

Windmiller


Edited by windmiller (08/18/07 02:45 PM)
Edit Reason: additional info
_________________________
We all live under one King

Top
2017 / 2014 NEC & Related Books and Study Guides
#167734 - 08/18/07 07:28 PM Re: 13.8 kV Cable Installation [Re: windmiller]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
328.10 & 328.12 Medium Voltage Cable

330.10b(4)MC uses primitted

300.37Requirements for over 600 Volts ,Nominal

Definitions read Exposed (as refered to un 300.37

My opinion No(must be underground or in a raceway or support system (tray) above ground. if subject to physical harm . Or Exposed to unqualified persons.