#167656 - 08/17/07 03:52 AM circuit phase Identification method
Angel_Electric Offline
Member
Registered: 06/03/07
Posts: 20
Loc: Fl.
I'm working more and more on three phase 120v 208v; 277v 480v applications I need a method of computing the circuit numbers into the phase of the circuit. Accuracy and efficiency is key.
I've been told there is a way to correlate the number with a multiplier and Identify the circuit phase. Any body ever heard of such methods or other applicable means would be greatly appreciated.
Top
Tools for Electricians:
#167657 - 08/17/07 04:11 AM Re: circuit phase Identification method [Re: Angel_Electric]
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
A company I worked for gave us all stickers the size of a business card with a chart of circuits 1 to 84 identified by phase and the colors we use.

We stuck them inside our hard hats, they also gave us laminated versions for our wallets.

In my opinion it was worth it, you can make them yourself on a PC.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#167684 - 08/17/07 04:54 PM Re: circuit phase Identification method [Re: iwire]
OUSoonerFan3 Offline
Junior Member
Registered: 07/13/06
Posts: 1
Divide circuit number by 6. Remainder will tell you what phase. 1 or 2 A phase, 3 or 4 B phase, 5 or no remainder C phase.
_________________________
Sean
Top
#167703 - 08/18/07 02:51 AM Re: circuit phase Identification method [Re: OUSoonerFan3]
Angel_Electric Offline
Member
Registered: 06/03/07
Posts: 20
Loc: Fl.
I appreciate the tips greatly.!!!
Top
#167773 - 08/19/07 08:24 PM Re: circuit phase Identification method [Re: Angel_Electric]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
The method posted by OUSoonerFan3 is what you were looking for - regarding the "Mathematical Way".
If you are good with Math, this will work great for 3 Phase "L-R" Circuitry (Circuitry in Panelboards, with Circuits on the "Left" and the "Right" sides).

It doesn't work with the following configurations:
  • Single Phase "L-R" Panels,
  • Panels / Gear with only a "Single Row" of Circuitry,
  • Power Panelboards with multipole Circuitry under the same "Number" - such as a 3 pole OCPD at the upper left of a Panelboard identifies A, B and C as "Circuit 1",
  • Panelboards with "Stack Breakers" or "Piggyback Breakers" - such as a "QO-20/20",
  • Old "Bulldog" / "Pushmatic" Panels


Iwire's response brings up a very good point - create color charts for various scenarios.

I have created a set of these in Excel, which you may use if needed.
Just E-amil me, and I will bounce it your way.

Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#168412 - 09/03/07 06:08 PM Re: circuit phase Identification method [Re: Scott35]
dadgene Offline
New Member
Registered: 09/02/07
Posts: 1
Loc: mo
Hello Scott i am new here and read your post on phase and circut identifiers color and # charts I would greatly like to get them charts!!! the cubs are drivin me!!! so would you please bounce em my way thank you EUGENE
Top
#168448 - 09/05/07 12:41 AM Re: circuit phase Identification method [Re: dadgene]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
dadgene

Send me an E-mail (so I can get your address), and I will pass on the spreadsheet to you.

Scott

BTW, my E-mail address may be found by either:
  1. Clicking on my user name in this reply (underlined link in the left pane),

    or
  2. Clicking on my username in the Moderator list at the bottom of this thread.


Me...
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#168505 - 09/06/07 04:39 PM Re: circuit phase Identification method [Re: Scott35]
Ralpha494 Offline
Member
Registered: 05/19/04
Posts: 73
Loc: Pewaukee,WI,USA
My method works whether the breakers are numbered the normal way (of odds on the left and evens on the right)or 1 to 21 on the left and 22 to 42 on the right. It just identifies C phase though. I just see if the number is a factor of six. Even numbers who's sum is divisible by 3 is how I've been doing it if I didn't have a chart. Examples: 30 even number 3+0=3; 54 even 5+4=9; 84 even 8+4=12; 102 even 1+0+2=3. So the normal numbering system identifies C phase on the right side only you have adjust accordingly. The other numbering system (1-21 on the left) just identifies every other one. So there.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals