#167650 - 08/16/07 07:45 PM Separately Derived Systems in the same pull box?
techgod Offline
Member
Registered: 12/15/03
Posts: 20
Loc: Burbank, Ca USA
I am currently installing a generator for optional standby loads in an office building. The Generator has two output breakers, one feeds a 120/208 ATS, the other feeds a 75kVA transformer near the generator for a 277/480V feed for a 277/480 ATS for the lighting loads. I also have a conduit with 277/480V feeders for a transformer & sub panel near the generator for the engine heater & battery charger ect. Can all of these conduits & feeders share the same junction box for an angle pull?

TIA,
Mark
Top
2017 / 2014 NEC & Related Books and Study Guides
#167654 - 08/17/07 03:27 AM Re: Separately Derived Systems in the same pull box? [Re: techgod]
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
Yes, being that this is an optional standby system.

Roger
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (sparkyinak), 108 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals