The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
Yesterday at 09:09 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 159 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#167650 - 08/16/07 07:45 PM Separately Derived Systems in the same pull box?
techgod Offline

Registered: 12/15/03
Posts: 20
Loc: Burbank, Ca USA
I am currently installing a generator for optional standby loads in an office building. The Generator has two output breakers, one feeds a 120/208 ATS, the other feeds a 75kVA transformer near the generator for a 277/480V feed for a 277/480 ATS for the lighting loads. I also have a conduit with 277/480V feeders for a transformer & sub panel near the generator for the engine heater & battery charger ect. Can all of these conduits & feeders share the same junction box for an angle pull?


2014 / 2011 NEC & Related Books and Study Guides
#167654 - 08/17/07 03:27 AM Re: Separately Derived Systems in the same pull box? [Re: techgod]
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Yes, being that this is an optional standby system.