#167605 - 08/16/07 04:48 AM Over/Under voltage problems
kenny2656 Offline
Junior Member
Registered: 03/09/04
Posts: 7
Loc: lake charles, la usa
Customer with serious over /under voltage problems .Local POCO has been less than helpful.Customer wants me to try to solve the problem.This is a residence-600 amp single phase service (3) 200 amp main breakers) 50KW generator w/auto transfer switch.The problem is the incoming voltage (240)gets out of balance example:(phase a =180 vac to ground, phase b =60 vac to ground. We know its a POCO problem, because when the customer has problems, others within a 2 block area have the same problem.I am considering installing a voltage relay with over/under voltage adjustments connected to a capacitor trip device connected to shunt trip main breakers.Has anyone here tried anything like this?
Opinions welcomed.
Top
Work Gear for Electricians and the Trades
#167611 - 08/16/07 08:21 AM Re: Over/Under voltage problems [Re: kenny2656]
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Sounds like classic open neutral.
_________________________
Earl
Top
#167619 - 08/16/07 01:15 PM Re: Over/Under voltage problems [Re: kenny2656]
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Originally Posted By kenny2656
Customer with serious over /under voltage problems .Local POCO has been less than helpful.Customer wants me to try to solve the problem.This is a residence-600 amp single phase service (3) 200 amp main breakers) 50KW generator w/auto transfer switch.The problem is the incoming voltage (240)gets out of balance example:(phase a =180 vac to ground, phase b =60 vac to ground. We know its a POCO problem, because when the customer has problems, others within a 2 block area have the same problem.I am considering installing a voltage relay with over/under voltage adjustments connected to a capacitor trip device connected to shunt trip main breakers.Has anyone here tried anything like this?
Opinions welcomed.


Sir, don't waste your time or the customer's money rigging up any fancy stuff. DEMAND that the POCO get their trouble guys out to find that open neutral before your client's house and the others go up in flames...you may also want to have the others experiencing problems also jump on the POCO about it.

This situation is very dangerous..let us know the outcome...
Top
#167624 - 08/16/07 03:01 PM Re: Over/Under voltage problems [Re: mxslick]
techie Offline
Member
Registered: 05/17/05
Posts: 246
Loc: palo alto, ca usa
If the local POCO drags their heels, invoke the magic words
"Public Utilities Commission" (or equivalent for your state). If they still drag their heels, file a complaint with the PUC.
Top
#167625 - 08/16/07 03:15 PM Re: Over/Under voltage problems [Re: techie]
techie Offline
Member
Registered: 05/17/05
Posts: 246
Loc: palo alto, ca usa
Top
#167627 - 08/16/07 03:23 PM Re: Over/Under voltage problems [Re: techie]
RODALCO Offline
Member
Registered: 12/08/05
Posts: 854
Loc: Titirangi, Akld, New Zealand
That is an open neutral problem there and can cause fires.
Most appliances, lights, TV's, electronic eq. don't like it and will burn out.

Demand that the POCO checks it's connections, at the TX, cables, and also the meter terminals.

Then the cables and terminations to the main distribution board have to be checked by the electrician (yourself).
_________________________
The product of rotation, excitation and flux produces electricty.
Top
#167631 - 08/16/07 03:53 PM Re: Over/Under voltage problems [Re: RODALCO]
Rewired Offline
Member
Registered: 01/01/06
Posts: 558
Loc: Hamilton, Ontario, Canada
Hust for ha'-ha's, what is the voltage line- line when this happens? if its steady at 240 then its almost guaranteed its a bad neutral.
My former employer had a problem identical to this. the problem was found to be a bad connection between right at the transformer bushing... One thing that tipped it off was we did an amprobe check at the main ground where it connects to the water line, zero amps was flowing.. If it were to have been a break elsewhere in the neutral you might see current flowing in the ground, taking a path through the water piping in the street then back through another ground in another building or through some other path back to the center-tap bushing of the transformer...

A.D
Top
#167674 - 08/17/07 01:56 PM Re: Over/Under voltage problems [Re: Rewired]
kenny2656 Offline
Junior Member
Registered: 03/09/04
Posts: 7
Loc: lake charles, la usa
Thanks for the replies. We have already determined the neutral problem is the fault of the POCO, but it has to be happening somehow on the primary side because many transformers are involved. They claim to be working on the problem.My customer is is not willing to wait for them to fix it.He wants protection on his side of the meter. Money is not a big issue, results are.
Top
#167706 - 08/18/07 04:46 AM Re: Over/Under voltage problems [Re: kenny2656]
Obsaleet Offline
Member
Registered: 04/05/03
Posts: 362
Loc: Pa
I would contact the POCO and give them 24hrs to straighten it out, or I call the PUC. I would also contact the nieghboring homes/business and urge them to contact POCO. Make lots of noise about the situation! Remind them if any equipment gets damaged you have instucted everyone concerned to call there insurance co. and lawyer up.
_________________________
Choose your customers, don't let them choose you.
Top
#167708 - 08/18/07 09:09 AM Re: Over/Under voltage problems [Re: Obsaleet]
George Offline
Member
Registered: 02/23/02
Posts: 375
Often a problem takes a while to fix.

---

I guess the Power Company could disconnect power until they find the problem.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals