#167562 - 08/15/07 10:42 AM Industrial 56" ceiling fan troubleshoot
bill woods Offline
Member
Registered: 11/21/01
Posts: 45
I am stumped! Here's the scenario. Two 56" 120V industrial ceilng fans in parallel. One speed control. These two fans are on phase one of a three phase system. Phase two and three are lighting circuits. All small loads. The fan closest to the rheostat drops out of service. Technician checks and the motor has been fried. Checks voltage while second fan is still running. Line to neutral reads 140V on load side of rheostat. Why? When the switch is in the "high" setting or the "low" setting voltage is 120V. When the switch is adjusted between these settings voltage reads 140V. Again why? I can't explain it to my staff cuz I am at a loss.
Top
Work Gear for Electricians and the Trades
#167563 - 08/15/07 10:47 AM Re: Industrial 56" ceiling fan troubleshoot [Re: bill woods]
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
The speed control works by chopping up the AC waveform, such that it is no longer a nice clean sine wave. Unless you use a "True RMS" multimeter, non-sinusoidal waveforms cause very screwy AC voltage readings in most cases.

Recheck the reading using a good quality TRMS meter, such as a Fluke 87.
Top
#167564 - 08/15/07 10:55 AM Re: Industrial 56" ceiling fan troubleshoot [Re: NJwirenut]
bill woods Offline
Member
Registered: 11/21/01
Posts: 45
The meter used was a Fluke 337. Brand new.
Top
#167567 - 08/15/07 11:51 AM Re: Industrial 56" ceiling fan troubleshoot [Re: bill woods]
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
I'll join you in stumpedness, then....:)

Does the working fan change speed properly between the high and low settings?

When you say the motor was "fried", do you mean actual burnt windings/smell, etc., or just an open connection with no visible damage?
Top
#167569 - 08/15/07 01:31 PM Re: Industrial 56" ceiling fan troubleshoot [Re: NJwirenut]
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
Could this be an issue of an open neutral, causing the other loads on phases B and C to affect the voltage on phase A?
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#167615 - 08/16/07 11:21 AM Re: Industrial 56" ceiling fan troubleshoot [Re: EV607797]
bill woods Offline
Member
Registered: 11/21/01
Posts: 45
Tech's troubleshooting reports no open neutral, and the fan has an open connection with no visible damage. He also reports that the fan housings seem a little on the warm side.
Top
#167616 - 08/16/07 12:02 PM Re: Industrial 56" ceiling fan troubleshoot [Re: bill woods]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
I just wondering is that ceiling fan is shared with common netrual with other lines if that so i will suggest that the fan run it own netural and Ø line as well because the fan speed control have it own ' modifed sine wave ' reduced voltage connection

Merci , Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#167620 - 08/16/07 01:22 PM Re: Industrial 56" ceiling fan troubleshoot [Re: bill woods]
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Originally Posted By bill woods
Tech's troubleshooting reports no open neutral, and the fan has an open connection with no visible damage. He also reports that the fan housings seem a little on the warm side.


Sounds like just a defective fan motor from here. A shifting neutral would probably have fried the motor violently and also killed the speed control.

As for your voltage readings, take them with a huge grain of salt, so to speak. If the control is electronic, in addition to chopping the wavewform, it would possibly increase the voltage to compensate for lost motor torque.

OTOH, you could have also been reading "inductive kickback" from the other fan's motor. smile

And as for the housings seeming "a little on the warm side" remember a normally operating modern motor can safely run up to 40 deg. C above ambient, more than hot enough to burn your hands!! smile

Replace the bad fan and move one..... smile
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals