The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
1 registered (Webmaster), 0 Guests and 69 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#167486 - 08/13/07 05:54 PM 445.18 Disconnect at Generator location & type
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
445.18 requires a disconnect at the Generator location. I read this to be a Fused or Breaker type . 240.21 Conductors must be protected at the point where they receive there supply. I feel the disconnect also should be close to the generator location. .other Opnions please??

Top
2017 / 2014 NEC & Related Books and Study Guides
#167490 - 08/13/07 07:30 PM Re: 445.18 Disconnect at Generator location & type [Re: Yoopersup]
wire_twister Offline
Member

Registered: 07/25/07
Posts: 265
Loc: Georgia USA
We sometimes put in generators for cell phone equipment, most are Generac sets. These have breakers on the gen-set where the conductors hook to the set, not what I consider accesseble though, they are inside the gen-set cabinet which is usualy locked.
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid

Top
#167575 - 08/15/07 04:23 PM Re: 445.18 Disconnect at Generator location & type [Re: wire_twister]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1308
Loc: Alaska
Be cafeful Jimmy by using the breaker that comes with the equipment. It may be considers as supplemental OCP thus does not meet protection requirements. It should state in the lititerture that come with the genset. I am not familar with Generac so you may be right and I may be wrong. The paperwork that come with out to tell you what size of diconnect to install. Also do not be a retard like my self who put the genset leads on the bottom lugs. The genset is the line not the load.
_________________________
"Live Awesome!" - Kevin Carosa

Top
#167578 - 08/15/07 04:57 PM Re: 445.18 Disconnect at Generator location & type [Re: sparkyinak]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
This is a very large Generator and came from the factory without a disconnect on it. Thus the question.Owner wants to install the disconnect same room aprox. 40-70 ft away,

Top
#167581 - 08/15/07 06:39 PM Re: 445.18 Disconnect at Generator location & type [Re: Yoopersup]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1308
Loc: Alaska
Closer the better, in sight of not to exceed 50 feet.
_________________________
"Live Awesome!" - Kevin Carosa

Top
#167591 - 08/15/07 10:56 PM Re: 445.18 Disconnect at Generator location & type [Re: sparkyinak]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9062
Loc: Estero,Fl,usa
How do you protect the conductors and the generator from a fault in that 50 feet? Are we assuming a short would stall the generator?
_________________________
Greg Fretwell

Top
#167610 - 08/16/07 08:16 AM Re: 445.18 Disconnect at Generator location & type [Re: gfretwell]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1308
Loc: Alaska
The disconnect needs to be close as practical not to exceed 50 feet. The 50 foot rule is somtimes it is not safe to be right at the equipment or if the equipment is elevated
_________________________
"Live Awesome!" - Kevin Carosa

Top
#167699 - 08/17/07 07:30 PM Re: 445.18 Disconnect at Generator location & type [Re: sparkyinak]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Show me the Code sections ? 50ft and within sight is in mtrs .This Generator is 13.8 volts .

Top
#167702 - 08/17/07 08:33 PM Re: 445.18 Disconnect at Generator location & type [Re: Yoopersup]
frenchelectrican Offline


Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
 Originally Posted By: Yoopersup
Show me the Code sections ? 50ft and within sight is in mtrs .This Generator is 13.8 volts .


if i am reading this right this is a low voltage or high votlage ??

13.8 volts or 13.8 KV ??

if it is 13.8 KV there is few other rules will show up with this type of voltage i am not too sure where it land but part of it will be not in the NEC

Merci , Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#167707 - 08/18/07 06:24 AM Re: 445.18 Disconnect at Generator location & type [Re: frenchelectrican]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
It is 13.8 KV and Yes it is part of the NEC as its in a hospital not utilty owned.

Top
Page 1 of 3 1 2 3 >


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals