I recently completed a service to a 4 slip dock and a month later, received a call from the builder of said dock who told me the owner reported to him feeling a tingle when he and his sons approached the metal ladder while swimming. The power distribution is as follows: The meter and house are at the top of the hill with 4-#2 Al conductors about 750 feet to a panel on the cliff above the dock. Fron this panel I ran 110' of 6-4 SOOW through the water to the dock.

With one lead of my meter attached to some bare wire in the water, the metal of the dock shows 2.75 Volts. The system ground wire is carrying 1.8 Amps and if I pull the ground wire off the bar I get 8 Volts to the dock metal. With the mains to the house, garage and dock off I still have the same current flow, yet neither the new copper ground rod at the meter, nor the poco ground, nor their guy wire show any current flow. I have of course started communication with the engineer at the 'lectric co, but he hasn't been out yet. Any ideas as to what's happening here? Am I correct in wanting to disconnect my ground wire until the power company figures out what's happening? Obviously this is the thing that the $ 200 an hour professionals (called attorneys) pay for their own places on the lake with, so I want to solve this situation before it worsens.
Top
Work Gear for Electricians and the Trades
#167418 - 08/12/07 06:28 AM Re: Ground wire leakage on boat dock [Re: Almost Fried]
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
Is the house connected by a metallic path to any other systems such as cable TV, city water, city gas, sewer lines, etc? Perhaps some other house is using your ground wire as a ground path.

Check if some of the current is flowing across the water main bond. Also check if current is flowing thru the bonding wires for the telephone system and cable system.
Top
#167422 - 08/12/07 07:27 AM Re: Ground wire leakage on boat dock [Re: Almost Fried]
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma

Here is a relevant thread over at Mike Holt:
http://forums.mikeholt.com/showthread.php?t=78799

In addition to checking for current flow from other systems as suggested above, also look for current flow between grounding electrodes.

-Jon
Top
#167424 - 08/12/07 09:05 AM Re: Ground wire leakage on boat dock [Re: winnie]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
This might just be regular ground shift. You may never figure out where it comes from but the utility is certainly a suspect. Bear in mind the dirt is always a parallel current path in a grounded system. Have you tried establishing a local ground electrode system at the dock, connected to your equipment grounding conductor?
_________________________
Greg Fretwell
Top
#167425 - 08/12/07 09:06 AM Re: Ground wire leakage on boat dock [Re: winnie]
gibbonsseabee80 Offline
Member
Registered: 10/10/05
Posts: 40
Loc: Chesapeake, VA
Hello,
I would check the service at the house first. Check the ground and the neutral/messenger at the house. It could be bad and all current running to the water. I put in ser and and 150amp diconnect/meter in my parents place a couple of years back. I cut free the service drop with gloves. When I reconnected the bare messenger first I got spark. When I finished my work, I looked at the neigbors house. Her messenger was broke and all the current was traveling through her water main and back through mine, out my messenger. Current loves the lowest resistance path home and just because the main is off in the house you are fed by, doesnt mean current can not come from a neighbors service. This is just some personal experience.
_________________________
Brian Gibbons
Top
#167434 - 08/12/07 10:44 AM Re: Ground wire leakage on boat dock [Re: gibbonsseabee80]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
I'm not saying that this is a code requirement anywhere BUT: The only system that I would let anyone I loved around would include a transformer at the boat slip. Naturally, the secondary Neutral would be bonded to a locally established ground. That's the same thing I would have done where they were shocking all the dairy cows in the remotely fed barn.
Joe
Top
#167466 - 08/12/07 06:29 PM Re: Ground wire leakage on boat dock [Re: JoeTestingEngr]
Almost Fried Offline
Member
Registered: 09/04/06
Posts: 98
Loc: Madison County, Ark. USA
Thank you all for your input and comments.

Cable is from a dish on the house. Water is from a well on the premises, haven't checked the ground current on that possibility. This home is quite a distance from other structures, the closest house is 1/4 mile away and on its own xfmr. A local ground would have to be bare wire into the lake as the shoreline is at best a few feet of gravel over bedrock. The dock is moored to an almost vertical cliff face. I have current flow through the steel cables extending down to the downriggers that space the dock from the shore.
Top
#167469 - 08/12/07 08:01 PM Re: Ground wire leakage on boat dock [Re: Almost Fried]
WESTUPLACE Offline
Member
Registered: 03/29/04
Posts: 251
Loc: Kingwood, TX USA
I assume there are NO boats connected to this system when you show the current. A miss-wired boat or shore cord will sure cause this problem. Robert
Top
#167470 - 08/12/07 08:02 PM Re: Ground wire leakage on boat dock [Re: Almost Fried]
Obsaleet Offline
Member
Registered: 04/05/03
Posts: 362
Loc: Pa
Are there any boats in the water connected to this power?
Ob
_________________________
Choose your customers, don't let them choose you.
Top
#167473 - 08/13/07 03:48 AM Re: Ground wire leakage on boat dock [Re: Obsaleet]
gibbonsseabee80 Offline
Member
Registered: 10/10/05
Posts: 40
Loc: Chesapeake, VA
Wow,
I am curious about this problem. The only thing I can think of is the dc battery system on the boat or the electrical on the boat itself. Maybe disconnect the negative on the dc battery system and turn shore power off and see if you have the same readings. Maybe a problem on the boat itself. Anyway, very interesting. Keep us posted when you figure it out.

Brian
_________________________
Brian Gibbons
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkyinak), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals