#167386 - 08/11/07 09:19 AM Arc Fault Circuits
CRM Offline
Member
Registered: 02/29/04
Posts: 74
Loc: Alberta Canada
I'm wiring a new house, are the walk in closet and master bedroom bathroom required to be arc fault protected. The way I read the code is, only the receptacles in the bedroom area are required. Also are the switch and light required to be arc fault protected in the bedroom area. Thanks for any help.
Top
Tools for Electricians:
#167441 - 08/12/07 12:00 PM Re: Arc Fault Circuits [Re: CRM]
mr_electrician Offline
Member
Registered: 06/22/07
Posts: 106
Loc: London, Ontario
The way to attack this is to connect all bedroom receptacles (maximum of 12) on the same circuit. Arc faults are expensive, so it is a good way of saving money and still meeting the code.
_________________________
Never trust an electrician with no eyebrows!!
Top
#167481 - 08/13/07 06:38 AM Re: Arc Fault Circuits [Re: CRM]
Rick Kelly Offline
Member
Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
To answer your questions... no, the light outlet and switch in a bedroom does not have to be fed from a AFCI protected circuit nor do the receptacles and outlets in a ensuite bathroom.

As to the walk in closet, does it have a door on it? If it does, then any receptacles installed in the closet do not need to be AFCI ptotected (unless some one sleeps in the closet). If the closet does not have a door on it then IMHO any receptacles installed in the closet do need to be AFCI protected.

Having said this... I agree with the above comment from mr_electrician.
Top
#168492 - 09/06/07 09:28 AM Re: Arc Fault Circuits [Re: Rick Kelly]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Well I would include a walk in or any closet as part of the bedroom and require an outlet in the closet to be AFCI protected. So why is there an outlet in the closet?
Top
#168534 - 09/07/07 06:23 PM Re: Arc Fault Circuits [Re: mikesh]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
Is "walk in closet" defined in the code? I've been treating them as ordinary rooms, if they have doors between them and the adjacent room. Plugs may be required by code and arc-fault protection isn't required. My thinking on the separate room issue is guided by the examples described in 26-712(f) and Appendix B 26-700(11).

However, I usually use the arc-fault circuit to feed that plug, because that circuit is already in the area. I just don't think the classification extends though a door, or hall plugs would have arc-fault protection.
Top
#168609 - 09/10/07 06:36 AM Re: Arc Fault Circuits [Re: twh]
Rick Kelly Offline
Member
Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
The code, at least the 2006 CEC, offers no definition of what is and is not a closet that I am aware of.

I am not sure how 26-712(f) helps to shine any light on this issue.

The question is, at least in my mind, when is a walk in closet not a closet and is in fact a room off of the bedroom. Maybe the number of square feet of the floor of a closet should be the guideline.

Interesting...
Top
#168616 - 09/10/07 09:12 AM Re: Arc Fault Circuits [Re: Rick Kelly]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
I asked several other inspectors and we agree that if the closet is off the bedroom we see it as part of the bedroom and not another room accessed through the bedroom so at least in this jurisdiction it is required to be AFCI protected. So ask your AHJ for their interpretation.
Top
#168632 - 09/10/07 09:15 PM Re: Arc Fault Circuits [Re: mikesh]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
The rule is worded "branch circuits that supply receptacles installed in sleeping facilities of a dwelling unit shall be protected by an arc-fault circuit interrupter."

"Sleeping facilities" appear to not include living-rooms, where people sleep on the sofa; dog houses, where bad spouses sleep; nor even attics with an only access being through a sleeping facility. The term doesn't include bathrooms. A bathroom isn't a sleeping facility. Nor does it include a water closet, nor any other type of closet.

When the drafters of the Canadian Electrical Code want to include adjacent rooms in the definition of "sleeping facilities", then can easily do so. Just as they have excluded adjacent rooms by simply not including them.

The code is adopted as law, and as such, we are entitled to apply it as written, using the ordinary meaning of the words - without asking each inspector how he applies each rule in his area. That's just the way laws are.

Appendix C9 deals specifically with the right to interpret the code. It doesn't matter how many inspectors line up, the Canadian Electrical Code excludes them from the right to interpret the code. For those who don't agree with the law, as written, Appendix C6 is a perfect solution.

Unless someone can point to a rule that includes an adjacent room as part of a "sleeping facility", the ordinary meaning of the words will exclude a closet; and, the sump pump in the closet in the basement bedroom need not be on an arc-fault circuit.
Top
#168726 - 09/13/07 09:55 AM Re: Arc Fault Circuits [Re: twh]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Originally Posted By twh
The rule is worded "branch circuits that supply receptacles installed in sleeping facilities of a dwelling unit shall be protected by an arc-fault circuit interrupter."

"Sleeping facilities" appear to not include living-rooms, where people sleep on the sofa; dog houses, where bad spouses sleep; nor even attics with an only access being through a sleeping facility. The term doesn't include bathrooms. A bathroom isn't a sleeping facility. Nor does it include a water closet, nor any other type of closet.

When the drafters of the Canadian Electrical Code want to include adjacent rooms in the definition of "sleeping facilities", then can easily do so. Just as they have excluded adjacent rooms by simply not including them.

The code is adopted as law, and as such, we are entitled to apply it as written, using the ordinary meaning of the words - without asking each inspector how he applies each rule in his area. That's just the way laws are.

Appendix C9 deals specifically with the right to interpret the code. It doesn't matter how many inspectors line up, the Canadian Electrical Code excludes them from the right to interpret the code. For those who don't agree with the law, as written, Appendix C6 is a perfect solution.

Unless someone can point to a rule that includes an adjacent room as part of a "sleeping facility", the ordinary meaning of the words will exclude a closet; and, the sump pump in the closet in the basement bedroom need not be on an arc-fault circuit.

TWH I am interpreting building code in whether a closet is part of the bedroom or another room. The building inspectors don't agree where a closet becomes a room. The building code says it is a dependant room and what does that mean? In any case where an interpretation of a code can require a lesser or greater requirement we usually side on the safer requirement.
So we interpret a closet to be a dependant room which is part of the bedroom and an outlet in a bedroom is required to be AFCI protected. No appeal of the CEC is possible but now you have me thinking about the building code and how it views a closet, walk in or hide in the corner when her husband comes home sized.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals