#167383 - 08/11/07 07:24 AM Single phase 480v lighting circuit
etech Offline
Member
Registered: 06/16/07
Posts: 17
Loc: Oregon
Need to install 3 480v single phase parking lot circuits on contactor. Can I get by with a 3 pole or do I need to go with a 6 pole? Must I break both conductors?
Top
Work Gear for Electricians and the Trades
#167384 - 08/11/07 07:39 AM Re: Single phase 480v lighting circuit [Re: etech]
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Originally Posted By etech
Need to install 3 480v single phase parking lot circuits on contactor. Can I get by with a 3 pole or do I need to go with a 6 pole? Must I break both conductors?


In my opinion 410.54(B) requires you to switch all ungrounded legs supplying the 'auxiliary equipment' (AKA the ballasts).
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#167385 - 08/11/07 07:43 AM Re: Single phase 480v lighting circuit [Re: iwire]
etech Offline
Member
Registered: 06/16/07
Posts: 17
Loc: Oregon
Thanks!
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals