The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
Potseal 7
sparky66wv 7
Who's Online
0 registered (), 282 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#166310 - 07/17/07 03:51 PM Humming in Cubicle of Medium Voltage Switchgear
windmiller Offline
Junior Member

Registered: 12/05/06
Posts: 43
Loc: Alaska
Hi,
I have noticed a humming that recently started in a section of medium voltage switchgear. it operates at 13.8 kV.

Could this be a harmonic imbalance or loose bus bar?

Thanks for any replies.

regards

Windmiller
_________________________
We all live under one King

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#166327 - 07/18/07 03:59 AM Re: Humming in Cubicle of Medium Voltage Switchgear [Re: windmiller]
Zog Offline
Member

Registered: 09/13/05
Posts: 116
Loc: Charlotte, NC
Yes, could be either of those or you could have tracking. If you can arrange a shutdown do it as soon as possible. A visual inspection of all insulating surfaces should be done looking for signs of tracking, use a black light for the inspection that will make it easier to find any traces of nitric acid.
If you cant shut down a visual inspection with a corona camera would be best.
_________________________
MV/HV Testing Specialist, "BKRMAN"

Top
#217356 - 06/24/16 04:46 AM Re: Humming in Cubicle of Medium Voltage Switchgear [Re: windmiller]
highvoltpower Offline
New Member

Registered: 06/23/16
Posts: 1
Loc: India
Surely, listen for popping, or cracking sounds produced by electrical discharges also humming sounds or vibration produced by quality. With lights out, look for blue or purple corona halos. Orange or red sputter arcs are created by intermittent sparking. Best way is you cannot blackout a graphic checkup with a halo.

Top
#217357 - 06/24/16 07:37 AM Re: Humming in Cubicle of Medium Voltage Switchgear [Re: windmiller]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Thermal imaging is a nice way to find problems like loose connections. The heat stays for a while after it's turned off so you have some time to look around.