The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 192 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#166310 - 07/17/07 03:51 PM Humming in Cubicle of Medium Voltage Switchgear
windmiller Offline
Junior Member

Registered: 12/05/06
Posts: 43
Loc: Alaska
Hi,
I have noticed a humming that recently started in a section of medium voltage switchgear. it operates at 13.8 kV.

Could this be a harmonic imbalance or loose bus bar?

Thanks for any replies.

regards

Windmiller
_________________________
We all live under one King

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#166327 - 07/18/07 03:59 AM Re: Humming in Cubicle of Medium Voltage Switchgear [Re: windmiller]
Zog Offline
Member

Registered: 09/13/05
Posts: 116
Loc: Charlotte, NC
Yes, could be either of those or you could have tracking. If you can arrange a shutdown do it as soon as possible. A visual inspection of all insulating surfaces should be done looking for signs of tracking, use a black light for the inspection that will make it easier to find any traces of nitric acid.
If you cant shut down a visual inspection with a corona camera would be best.
_________________________
MV/HV Testing Specialist, "BKRMAN"

Top
#217356 - 06/24/16 04:46 AM Re: Humming in Cubicle of Medium Voltage Switchgear [Re: windmiller]
highvoltpower Offline
New Member

Registered: 06/23/16
Posts: 1
Loc: India
Surely, listen for popping, or cracking sounds produced by electrical discharges also humming sounds or vibration produced by quality. With lights out, look for blue or purple corona halos. Orange or red sputter arcs are created by intermittent sparking. Best way is you cannot blackout a graphic checkup with a halo.

Top
#217357 - 06/24/16 07:37 AM Re: Humming in Cubicle of Medium Voltage Switchgear [Re: windmiller]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
Thermal imaging is a nice way to find problems like loose connections. The heat stays for a while after it's turned off so you have some time to look around.