The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 200 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#166001 - 07/09/07 07:21 PM Phantom voltage affecting motion switch
Haligan Offline
Member

Registered: 02/25/04
Posts: 112
Loc: Berkeley, CA USA
I have an occupancy detector switch controlling a split 15a rec. (top half always hot, bottom half switched. )
A very low resistive lighting load is plugged into the rec.
When the switch is set to Auto, the light is always on (low power). I swapped out that load with an incandescent lamp and the switch operates as expected.
My meter is reading 2-3 volts from the recep when the switch is on Auto and no motion is present.
Circuit is grounded all the way to panel.

I figure my options are:
1. Put the switched recep in its own box. It's in a 2gang box with another recep.
2. Find a way to add resistance to the low light load.
3. Try another switch.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#166003 - 07/09/07 07:29 PM Re: Phantom voltage affecting motion switch [Re: Haligan]
JCooper Offline
Member

Registered: 12/30/02
Posts: 229
Loc: Kendall Park, NJ USA
You may be seeing leakage from your switch, not induced voltage from the adjacent cable

Top
#166006 - 07/09/07 08:10 PM Re: Phantom voltage affecting motion switch [Re: JCooper]
Haligan Offline
Member

Registered: 02/25/04
Posts: 112
Loc: Berkeley, CA USA
That narrows it down to #2 and #3.

Top
#166017 - 07/10/07 09:54 AM Re: Phantom voltage affecting motion switch [Re: Haligan]
Jonno Offline
Member

Registered: 05/27/06
Posts: 20
The sensor is deriving power from the AC line through the load. The sensor needs power all the time to be able to detect motion, and as a result lets a few mA leak through the load to power itself. With incandesant lighting this is unnoticable and not an issue. If you read the spec. sheet these sensors typicaly call for connection to permenant incandessant fixtures (not plug and cord connected). With an incandesant fixture (there may be a minimum wattage specified) it will work fine.

I know this is not a solution but it should atleast help you understand the problem. It is nothing to do with your wiring methods.

Top
#166022 - 07/10/07 01:09 PM Re: Phantom voltage affecting motion switch [Re: Jonno]
Haligan Offline
Member

Registered: 02/25/04
Posts: 112
Loc: Berkeley, CA USA
I'll check the spec sheet. Letsee here, French, German, Spanish, Swahili, aha! English!

Yep. that was it. I called Leviton. They have a relay- driven sensor switch. I'll swap it out for that one.

thx