#166001 - 07/09/07 07:21 PM Phantom voltage affecting motion switch
Haligan Offline
Member
Registered: 02/25/04
Posts: 111
Loc: Berkeley, CA USA
I have an occupancy detector switch controlling a split 15a rec. (top half always hot, bottom half switched. )
A very low resistive lighting load is plugged into the rec.
When the switch is set to Auto, the light is always on (low power). I swapped out that load with an incandescent lamp and the switch operates as expected.
My meter is reading 2-3 volts from the recep when the switch is on Auto and no motion is present.
Circuit is grounded all the way to panel.

I figure my options are:
1. Put the switched recep in its own box. It's in a 2gang box with another recep.
2. Find a way to add resistance to the low light load.
3. Try another switch.
Top
Work Gear for Electricians and the Trades
#166003 - 07/09/07 07:29 PM Re: Phantom voltage affecting motion switch [Re: Haligan]
JCooper Offline
Member
Registered: 12/30/02
Posts: 228
Loc: Kendall Park, NJ USA
You may be seeing leakage from your switch, not induced voltage from the adjacent cable
Top
#166006 - 07/09/07 08:10 PM Re: Phantom voltage affecting motion switch [Re: JCooper]
Haligan Offline
Member
Registered: 02/25/04
Posts: 111
Loc: Berkeley, CA USA
That narrows it down to #2 and #3.
Top
#166017 - 07/10/07 09:54 AM Re: Phantom voltage affecting motion switch [Re: Haligan]
Jonno Offline
Member
Registered: 05/27/06
Posts: 20
The sensor is deriving power from the AC line through the load. The sensor needs power all the time to be able to detect motion, and as a result lets a few mA leak through the load to power itself. With incandesant lighting this is unnoticable and not an issue. If you read the spec. sheet these sensors typicaly call for connection to permenant incandessant fixtures (not plug and cord connected). With an incandesant fixture (there may be a minimum wattage specified) it will work fine.

I know this is not a solution but it should atleast help you understand the problem. It is nothing to do with your wiring methods.
Top
#166022 - 07/10/07 01:09 PM Re: Phantom voltage affecting motion switch [Re: Jonno]
Haligan Offline
Member
Registered: 02/25/04
Posts: 111
Loc: Berkeley, CA USA
I'll check the spec sheet. Letsee here, French, German, Spanish, Swahili, aha! English!

Yep. that was it. I called Leviton. They have a relay- driven sensor switch. I'll swap it out for that one.

thx
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 20 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals