The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 245 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#165995 - 07/09/07 03:51 PM MC Vs Conduit
JoeRossi Offline
Member

Registered: 01/31/03
Posts: 26
Loc: Washington, NJ
Is mc concidered conduit?
Do you have an support one way or another?
Thanks for you help
_________________________
Joe Rossi

Top
2014 / 2011 NEC & Related Books and Study Guides
#165996 - 07/09/07 04:09 PM Re: MC Vs Conduit [Re: JoeRossi]
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Joe, MC cable is considered cable.
It must be supported and secured at intervals not over 6', and if 4 or fewer conductors #10 or smaller, must be secured within a foot of any fitting or termination.
Exceptions are where it's fished, or fixture whips up to 6' long.

See Article 330--especially 330.30

Top