The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Potseal 7
Who's Online
0 registered (), 279 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#165995 - 07/09/07 03:51 PM MC Vs Conduit
JoeRossi Offline
Member

Registered: 01/31/03
Posts: 26
Loc: Washington, NJ
Is mc concidered conduit?
Do you have an support one way or another?
Thanks for you help
_________________________
Joe Rossi

Top
2014 / 2011 NEC & Related Books and Study Guides
#165996 - 07/09/07 04:09 PM Re: MC Vs Conduit [Re: JoeRossi]
electure Offline

Member

Registered: 12/24/00
Posts: 4225
Loc: Fullerton, CA USA
Joe, MC cable is considered cable.
It must be supported and secured at intervals not over 6', and if 4 or fewer conductors #10 or smaller, must be secured within a foot of any fitting or termination.
Exceptions are where it's fished, or fixture whips up to 6' long.

See Article 330--especially 330.30

Top