The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 216 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#165995 - 07/09/07 03:51 PM MC Vs Conduit
JoeRossi Offline

Registered: 01/31/03
Posts: 26
Loc: Washington, NJ
Is mc concidered conduit?
Do you have an support one way or another?
Thanks for you help
Joe Rossi

2014 / 2011 NEC & Related Books and Study Guides
#165996 - 07/09/07 04:09 PM Re: MC Vs Conduit [Re: JoeRossi]
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Joe, MC cable is considered cable.
It must be supported and secured at intervals not over 6', and if 4 or fewer conductors #10 or smaller, must be secured within a foot of any fitting or termination.
Exceptions are where it's fished, or fixture whips up to 6' long.

See Article 330--especially 330.30

#166507 - 07/22/07 03:01 PM Re: MC Vs Conduit [Re: electure]
teester Offline

Registered: 07/21/07
Posts: 34
Loc: SC
Ah, that dang NEC...