#165995 - 07/09/07 03:51 PM MC Vs Conduit
JoeRossi Offline
Member
Registered: 01/31/03
Posts: 26
Loc: Washington, NJ
Is mc concidered conduit?
Do you have an support one way or another?
Thanks for you help
_________________________
Joe Rossi
Top
2017 / 2014 NEC & Related Books and Study Guides
#165996 - 07/09/07 04:09 PM Re: MC Vs Conduit [Re: JoeRossi]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Joe, MC cable is considered cable.
It must be supported and secured at intervals not over 6', and if 4 or fewer conductors #10 or smaller, must be secured within a foot of any fitting or termination.
Exceptions are where it's fished, or fixture whips up to 6' long.

See Article 330--especially 330.30
Top
#166507 - 07/22/07 03:01 PM Re: MC Vs Conduit [Re: electure]
teester Offline
Member
Registered: 07/21/07
Posts: 34
Loc: SC
Ah, that dang NEC...
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals