The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
failed home inspection.
by HotLine1
01/19/17 01:41 PM
Safety at heights?
by Trumpy
01/19/17 05:25 AM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
Search Function
by Webmaster
01/18/17 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 09:17 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
1 registered (Ruben Rocha), 0 Guests and 205 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#165861 - 07/06/07 01:21 PM conductor inductance
barbwire Offline
Junior Member

Registered: 05/15/03
Posts: 17
O.K. next question, I have a 110/208 volt sw gear with 2 sections, feeding out to 6 closets are 2 sets of 400 amp feeders,paralleled, (fed underground), if I want to keep a good pattern in my riser bank I may have to utilize two conduits in different sections of gear, they come out of the ground about 4 ft apart, as long as I keep the conductors together out of each conduit does this comply with 300-20?

Top
2017 / 2014 NEC & Related Books and Study Guides
#165887 - 07/06/07 11:11 PM Re: conductor inductance [Re: barbwire]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9063
Loc: Estero,Fl,usa
You didn't say if these were metal raceways but if you keep the conductor sets grouped it really doesn't make any difference. Keep all the conductors from each circuit in one pipe. Where you have parallel sets, keep each set together (A/B/C/N in one pipe A/B/C/N from the parallel set in another pipe)
All of the "Goes Outtas" have to balance all of the "Goes Innas"
_________________________
Greg Fretwell

Top
#165897 - 07/07/07 07:18 AM Re: conductor inductance [Re: gfretwell]
barbwire Offline
Junior Member

Registered: 05/15/03
Posts: 17
Sorrry, raceways are PVC underground with a change over to rigid coming through the slab. Thanks for the reply, makes sense.

Top