#165761 - 07/05/07 04:56 AM Best method for attaching 500MCM to rope?
mr_electrician Offline
Member
Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Hey gent's, can anyone share with me the best method to use when attaching a rope to 3 - 500 MCM cables. I am pulling 180' with 2 90's, and 2 30 degree bends. I am thinking of attaching 3 kellum grips (1 for each), but I am worried that they may slip off! What do you think?
_________________________
Never trust an electrician with no eyebrows!!
Top
Tools for Electricians:
#165762 - 07/05/07 05:19 AM Re: Best method for attaching 500MCM to rope? [Re: mr_electrician]
Navyguy Offline
Member
Registered: 10/14/05
Posts: 29
Loc: Welland, Ontario, Canada
I have used grips in the past with great success. The key is that you must stagger the grips on the pull rope. I splice one at the very end and then I have several others spliced further along the rope. I also take a strand from each “side” of the conductor and bend it out side of the grip so that I will not “drop” one in the pipe. Use lots of tape and lube.

Cheers


Edited by Navyguy (07/05/07 05:20 AM)
Top
#165763 - 07/05/07 05:26 AM Re: Best method for attaching 500MCM to rope? [Re: Navyguy]
mr_electrician Offline
Member
Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Awsome, thanks for the confirmation, Looks like being out of construction for 5 years has not taken a toll on me yet.
_________________________
Never trust an electrician with no eyebrows!!
Top
#165766 - 07/05/07 05:41 AM Re: Best method for attaching 500MCM to rope? [Re: mr_electrician]
Hendrix Offline
Junior Member
Registered: 01/12/07
Posts: 22
Loc: NH
Are kellum grips those Chineese finger thingies you used as a kid? If so, I agree with Navyguy.
Top
#165788 - 07/05/07 11:45 AM Re: Best method for attaching 500MCM to rope? [Re: Hendrix]
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
Yes, "Kellem" grips are Hubbell's brand of a "Chinese finger". When sized and used correctly, they won't let go. The key is the length of the grip, not the diameter. Way too often, people spread these things open wider than they should, resulting in less pulling grip. I can take one designed for up to 1/2" and force it onto a piece of 750, but the grip range length is reduced to half of what it should be. THAT's were failures occur.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals