The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 99 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#165669 - 07/02/07 06:32 PM Subpanel Location
kinetic Offline
Member

Registered: 04/06/02
Posts: 158
Loc: Phoenix, Arizona
I had some copper thieves cut all of my homeruns in a residential job I am working on. The easiest fix is to run the wires into a couple of subpanels. Most will be long enough to reach but the only place for subpanels is in a large walk in closet. I will be able to retain my working clearances and the nearest shelving will be 2ft away from the closest panel location. Anyway around 240-24(d) or am I looking at replacing all my homeruns in the house?

Top
2014 / 2011 NEC & Related Books and Study Guides
#165670 - 07/02/07 06:40 PM Re: Subpanel Location [Re: kinetic]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Only place is in the forbidden closet? nonsense.

Hallways. Stairwell landings. Garage. Laundry room. Kitchen. There is no shortage of good places.

Want an easy way to hide it? Place it where an open door will block the view.

Top
#165672 - 07/02/07 07:09 PM Re: Subpanel Location [Re: renosteinke]
kinetic Offline
Member

Registered: 04/06/02
Posts: 158
Loc: Phoenix, Arizona
Hallways are full of arched niches, garage was the orginal location, single story house, laundry room on the opposite end of the house. The layout of the house has all the bedrooms on the panel side of the house. The main living spaces in the middle and any mechanical rooms, laundry rooms, etc. on the opposite side. Do large walk in closets really pose that much of a problem? I have seen more combustible material next to a garage subpanel than I care to see. I would put the panels behind the doors to keep them from being blocked. This house was a bear for long wire pulls and really not looking foward to repulling all of the homeruns. Hoping I might find a grey area.

Top
#165675 - 07/02/07 08:15 PM Re: Subpanel Location [Re: kinetic]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You could put J boxes in the closets and extend to the original panel.
_________________________
Greg Fretwell

Top
#165677 - 07/03/07 02:42 AM Re: Subpanel Location [Re: gfretwell]
Chris Simms Offline
Member

Registered: 03/10/05
Posts: 34
Loc: Cohutta Ga
The last house that I wired was a 400 amp service and they stole my panels (cut the wire just above the panels) and I contacted my local county inspecter and told him what I was planning to do. I took a smaller 100 amp panel and gutted it out and mounted it above the new panel and used this as a large junction box. I simply put connectors in the top and bottom and extended the wire. This was actually in the basement bu the covers that come with the small panels dont look to bad ( I just didn't remove any of the cover knock outs) Plassed with no problems
Chris

Top
#165682 - 07/03/07 05:23 AM Re: Subpanel Location [Re: Chris Simms]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
240-24(D) doesn't leave a lot of gray...it just says "no way".
_________________________
Ghost307

Top
#165705 - 07/03/07 02:06 PM Re: Subpanel Location [Re: ghost307]
ChicoC10 Offline
Member

Registered: 05/30/07
Posts: 169
Loc: CA
Out of curiosity, does anyone know what year 240.24(d) was added to the code?
I'm constantly coming across fuseboxes, old XO and Zinsco type subs in entry, hall, and bedroom closets. Even in cupboards. It seems as though this must have been an accepted practice back when.

Top
#165708 - 07/03/07 03:19 PM Re: Subpanel Location [Re: ChicoC10]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
"easily ignited" has been in the code virtually forever but the "clothes closet" part was added in the 80s
_________________________
Greg Fretwell

Top
#166027 - 07/10/07 02:47 PM Re: Subpanel Location [Re: gfretwell]
kinetic Offline
Member

Registered: 04/06/02
Posts: 158
Loc: Phoenix, Arizona
Is there a stipulation as when a "clothes closet" becomes a room....such as size? Some of these closets a so massive they really become much more than a simple closet with bifold doors.

The inspector allowed me to make lockable cabinet doors with a face frame to cover the panels.

Top
#166028 - 07/10/07 03:16 PM Re: Subpanel Location [Re: kinetic]
JJM Offline
Member

Registered: 10/31/05
Posts: 102
I appears "easiest" is the operative word, but why does "easist" have to be part of the equation?

You originally decided on those homeruns for a reason, so why should you let some thief change your entire wiring plan? Anyone else who looks at this job and see's this box of wire nuts will no doubt wonder what kind of hack did this.

It's your reputation and licens, I know it's a real bummber to redo those homeruns but you shouldn't be looking for shortcuts on a brand new wiring job.

Joe

Top