The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
01/19/17 09:52 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
2 registered (Ruben Rocha, gfretwell), 0 Guests and 185 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#165567 - 06/30/07 11:43 AM 90 Degree EMT Wire Pull Connector In Wall?
InspectorE Offline
Member

Registered: 10/08/04
Posts: 51
Loc: Hudson WI USA
Is it code compliant to use a 90 degree EMT wire pull as a sharp right angle turn through a wall? The construction is structural insulated panel with 2x2 furring strips. There isn't enough room to simply use a conduit bender, but a sharp 90 degree would work. The 90 degree wire pull EMT connector will work physically, but can it be used in this application? The wire pull is NOT needed due to the 360 degree total turn limit.

The wire pull is certainly rated for use where it is accessible; the question is can it be used where it is not necessary to be accessible? This is kind of like a doctor prescribing a drug for "off label use". If not acceptable, can you quote a NEC section?

Thanks guys

Frank

Top
2017 / 2014 NEC & Related Books and Study Guides
#165568 - 06/30/07 12:15 PM Re: 90 Degree EMT Wire Pull Connector In Wall? [Re: InspectorE]
gfretwell Online   content


Member

Registered: 07/20/04
Posts: 9065
Loc: Estero,Fl,usa
300.15(A) "...The covers shall be accessible after installation"
300.18 Raceway Installations.
(A) Complete Runs. Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete between outlet, junction, or splicing points prior to the installation of conductors.
_________________________
Greg Fretwell

Top
#165685 - 07/03/07 05:56 AM Re: 90 Degree EMT Wire Pull Connector In Wall? [Re: InspectorE]
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Originally Posted By InspectorE
"90 degree EMT wire pull"


Do you mean an LB, LL, LR, or "Pulling Ell"? If so, the answer is no.

I ask because there are still some short radius benders out there that still fit the bill for the listed radidus in the code.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#165686 - 07/03/07 07:16 AM Re: 90 Degree EMT Wire Pull Connector In Wall? [Re: e57]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
He might mean a 90 flex connector ... which I have seen used on EMT frown

The short answer ... if you can't pull wires through it, you can't bury it.

Top