#165529 - 06/29/07 03:22 PM Transformer hit by lightning
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
This picture submitted by ECN Member Richard:
Top
Tools for Electricians:
#165563 - 06/30/07 09:42 AM Re: Transformer hit by lightning [Re: Trumpy]
richard Offline
Member
Registered: 08/07/03
Posts: 94
Loc: L.I. New York
I guess i should give some info on this. This transformer feeds a major bookstore that is in most if not all states in the u.s.
The batteries gave out after 25 min. and the 1200 amp backup gen. failed. After change out of the gen. breaker, the store was back online. Also, they will have to see if the batteries will have to be replaced, due to weakening from the lightning strike.
Top
#165575 - 06/30/07 03:00 PM Re: Transformer hit by lightning [Re: richard]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
richard,
Are those wires on that transformer supposed to be bare?. crazy
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#165586 - 06/30/07 07:08 PM Re: Transformer hit by lightning [Re: Trumpy]
techie Offline
Member
Registered: 05/17/05
Posts: 246
Loc: palo alto, ca usa
The bare wires that I see look like concentric shields..
Top
#165600 - 07/01/07 07:48 AM Re: Transformer hit by lightning [Re: techie]
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Wow, either the lightning blew H1A's bushing completely out of the tank or someone disconnecting it did. I am not sure because H1C is grounded out which someone would have to do with a hot stick. There is oil all over the tank from H1A's bushing well, if that one was done with a hot stick it's probably all over the operator too.

Edit-Upon closer examination H1C's bushing is capped and the cap has a brown charred look like the rest of the equipment. It must not have been connected. Also, H2A's bushing looks broken and about to fall off. Seems like A phase took it pretty hard.


Edited by Nick (07/01/07 07:53 AM)
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 75 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals