The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 299 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#165489 - 06/28/07 04:46 PM 6' fixture whips
bman Offline

Registered: 07/07/06
Posts: 20
Loc: or
Installed some drop in lights the other day and noticed the whips I used to attach were labled 18/2 7amps max load. They were UL listed, am wondering if anyone knows if the listing permits a "feed thru" load (IE fixture to fixture) or is it just J-box to singal fixture only.

2014 / 2011 NEC & Related Books and Study Guides
#165493 - 06/28/07 05:38 PM Re: 6' fixture whips [Re: bman]
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
You really need to see the manufacturers' instructions. While the use of #18 suggests that the whips are intended to be run from J-Box to light only, some such assemblies have several circuits in the whip, and connectors designed to make the connection 'at,' rather then 'in' the fixture.