The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 208 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#165461 - 06/28/07 07:41 AM SE conductor extension
bman Offline
Member

Registered: 07/07/06
Posts: 20
Loc: or
Have a 1200A 480V service board in dedicated electrical room. Would like to tap bus and extend conductors via conduit out top of said board across ceiling and terminate into fused SE rated disconnect switch. Installation would meet depth of working clearance and 25' tap rule. Concern is art. 230.70. Is this code legal?

Top
2014 / 2011 NEC & Related Books and Study Guides
#165469 - 06/28/07 09:18 AM Re: SE conductor extension [Re: bman]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
230.70(A) means whatever your AHJ says it means and you have to ask him. I don't think what you say will fly but that is a 3000 mile away opinion.
_________________________
Greg Fretwell

Top
#165474 - 06/28/07 10:34 AM Re: SE conductor extension [Re: gfretwell]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Even if 230.70(A)(1) is not a problem, 230.72(A) may be. I would not consider a service disconnet on a different wall as being grouped with the other disconnect(s).
_________________________
Don(resqcapt19)

Top
#165475 - 06/28/07 11:22 AM Re: SE conductor extension [Re: resqcapt19]
Elec N Spec Offline
Member

Registered: 07/06/06
Posts: 33
Loc: Rochester Hills, MI USA
Your AHJ may have a problem with 110.3 (B). You are tapping or altering a piece of listed equipment. The manufacturer of the equipment may void it’s listing if it is altered in anyway.

Regards,


Elec N Spec

Top
#165477 - 06/28/07 01:42 PM Re: SE conductor extension [Re: Elec N Spec]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
110.3(B) can bite you in the butt.
If you modify the bus in the field, the UL Listing is no longer valid; even if the manufacturer blesses your method.
If you decide to go ahead, you should plan on paying UL for a field inspection to certify that the board retains its UL Listing. Otherwise the AHJ can turn down the whole job.
_________________________
Ghost307

Top
#165478 - 06/28/07 01:52 PM Re: SE conductor extension [Re: ghost307]
Elec N Spec Offline
Member

Registered: 07/06/06
Posts: 33
Loc: Rochester Hills, MI USA
I have enforced this. That is why I brought it up.

Elec N Spec

Top
#165480 - 06/28/07 02:05 PM Re: SE conductor extension [Re: Elec N Spec]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
UL has specifically stated that unless the equipment is listed for a field tap using manufacturer supplied materials, then it would not be within the listing to tap the bus.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#165482 - 06/28/07 03:02 PM Re: SE conductor extension [Re: Tom]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Last time I ran into a similar situation....a phone call to the Mfg. (CH), a field engineer arrived, looked, measured, sketched. 24 hours later I had Eng. signed/sealed drawings, and costs.

Came time to install, Factory Field guys came, fabricated a few extra bends, and made it work.
AHJ at site, looked, took copy of drawings & cert., left Approval sticker & cut-in card.

BTW, the overall $$$ was not that bad, considering what they did, plus the install.
John

PS: The same services are available from other mfg's, you just have to track down the right contacts.
_________________________
John

Top
#165488 - 06/28/07 04:39 PM Re: SE conductor extension [Re: HotLine1]
bman Offline
Member

Registered: 07/07/06
Posts: 20
Loc: or
Thanks for the input. I have a call into the inspector, should hear back in the morning, will let you know what he says.

Top
#165521 - 06/29/07 01:38 PM Re: SE conductor extension [Re: bman]
Elec N Spec Offline
Member

Registered: 07/06/06
Posts: 33
Loc: Rochester Hills, MI USA
Good luck. You gents are on the ball. I am seeing more and more non-listed equipment, fixtures and devices out in the field and some contractors have been hurt badly by basing their bids on equipment that they can’t use. Some time a real bargain can cost you more than what you were planning to save in the first place.
Regards,
Elec N Spec