#165386 - 06/26/07 04:25 PM Burnt romex
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
I was troubleshooting a burning smell when I pulled back a piece of paper-backed insulation. The insulation had a black mark about 18" long where the romex had burned it, and the romex had brown burn marking on the romex for about 18". (These are 120 volt fluorescent fixtures with magnetic ballasts). The ballasts were very hot to the touch but the whole circuit was drawing 4 amps. My thoughts are that the heat from the ballasts caused the burning. Has anyone else come across this before?
Top
Work Gear for Electricians and the Trades
#165400 - 06/26/07 10:58 PM Re: Burnt romex [Re: sid123456]
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
The answer depends on where the romex was in relation to the ballasts..was it touching them directly or laying on the fixture? And did the burn marks line up with the ballast location? If not, then there is some other issue at work here....and note that a standard magnetic ballast can run very hot to touch normally.

And did you get and pictures? smile





Edited by mxslick (06/26/07 10:59 PM)
Edit Reason: To fix ballast from "balls" oops!
_________________________
Stupid should be painful.
Top
#165405 - 06/27/07 12:16 AM Re: Burnt romex [Re: sid123456]
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Originally Posted By sid123456
'The ballasts were very hot to the touch'..


Well how hot were they? Sounds like too hot.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#165432 - 06/27/07 03:34 PM Re: Burnt romex [Re: e57]
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
The romex was in the attic. There was sheetrock between the wire and the fixture with insulation on top of the wire (paper-backed). With the wire only being burnt about 18" past both fixtures, I think the copper transfered the heat from the ballasts that far, and the insulation kept the heat from dissipating. Sorry no pictures. I need to take my camera with me, that would be a great idea.
Top

Member Spotlight
Member Since: 05/03/03
Posts: 1137
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals