The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (LongRunner), 218 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#165024 - 06/16/07 02:01 PM Transformer inrush
ChrisKennedy Offline
New Member

Registered: 06/10/07
Posts: 4
Loc: Miami Fla
1st post. How do you calc transformer inrush current?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#165028 - 06/16/07 03:48 PM Re: Transformer inrush [Re: ChrisKennedy]
gibbonsseabee80 Offline
Member

Registered: 10/10/05
Posts: 40
Loc: Chesapeake, VA
Hello Chris,
This is a big formula that has some symbols that can not be typed in this block. I found a link for you. Maybe this will will help you out. I breaks it all down.
http://www.transformerscommittee.org/info/F01/IEEE_Inrush_Tutorial.pdf
_________________________
Brian Gibbons

Top
#165036 - 06/16/07 09:01 PM Re: Transformer inrush [Re: gibbonsseabee80]
ChrisKennedy Offline
New Member

Registered: 06/10/07
Posts: 4
Loc: Miami Fla
Thanks Brian, looks like what I need.

Top
#165045 - 06/17/07 12:09 AM Re: Transformer inrush [Re: ChrisKennedy]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
OK Chris so you are looking to know what the inrush current on a MVA transformer, should be?.
Is this for the purposes of fusing or cable sizing?.
I personally think you are out of your depth, if you have to ask the question in the first place.
Just my opinion.
Cheers,
Mike.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#165046 - 06/17/07 03:16 AM Re: Transformer inrush [Re: Trumpy]
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Originally Posted By: Trumpy
I personally think you are out of your depth, if you have to ask the question in the first place.


What the heck does that mean?

He should not try to learn something new?

I 'know' Chris from another forum, he is a competent professional who appears he wants to expand his knowledge of the trade.

It happens that here under the NEC we can be capable of overcurrent device and conductor sizing for transformers without actually knowing how to calculate the actual inrush currents.

Mike, do you know how to calculate the actual inrush currents for a particular transformer?

I don't, but I am not out of my depth when I have to choose overcurrent protection for a transformer installation.


Edited by iwire (06/17/07 03:17 AM)
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#165051 - 06/17/07 05:49 AM Re: Transformer inrush [Re: Trumpy]
ChrisKennedy Offline
New Member

Registered: 06/10/07
Posts: 4
Loc: Miami Fla
 Originally Posted By: Trumpy

Is this for the purposes of fusing or cable sizing?.


In part,yes. The two things I love most about my work are when the lights on a big project come on for the first time and the sound of a large transformer being energized. The sound of the inrush. I want to know whats happening at that moment.
Thanks all for your help and opinions.

Top
#165083 - 06/17/07 09:12 PM Re: Transformer inrush [Re: ChrisKennedy]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Chris,
I would like to un-reservedly apologise for the nasty reply I provided you with last night.
This sort of behaviour, I'm not proud of at all.
Sorry to anyone else that read my reply also,
this will not be happening again.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#165088 - 06/17/07 11:11 PM Re: Transformer inrush [Re: Trumpy]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Having read the PDF file from Brian, that top formula seems wildly familiar.
With that said, is an inrush current sinusoidal? (as in a pure sine wave?).
We wind our own transformers at work (PoCo) and one part of my Linemans apprenticeship was 6 months in the Transformer shop, which I only go into these days if it's too cold in the Faultsman's office!. \:D
I must ask our head Transformer guy at work how they calculate the inrush current, because we get a Post-It note tacked to the side of the tranny stating what size fusing to use, for both run and in-rush current.
Bear in mind Chris, we use totally different voltages here in New Zealand, but the formula should still hold true.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#165101 - 06/18/07 09:41 AM Re: Transformer inrush [Re: Trumpy]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Pardon my ignorance but why wouldn't you have inrush on every cycle? I guess I don't understand all I know about transformers.
_________________________
Greg Fretwell

Top
#165103 - 06/18/07 09:48 AM Re: Transformer inrush [Re: gfretwell]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Once the transformer is started there is always a residual magnetic field to control the incomming current. IE it opposes the incomming rush of current. When a transformer is energised there is no magnetic opposition to the flow of current hence the Inrush. Once the transformer has an established magnetic field the 0 crossing of the AC does not cause a complete collapse of the opposing EMF and magnetic field.


Edited by mikesh (06/18/07 09:50 AM)
Edit Reason: spelling

Top