#164980 - 06/15/07 05:08 PM Sizing of service lateral from 320 Amp meter base?
homer Offline
Member
Registered: 09/30/04
Posts: 68
Loc: Vancouver, WA, USA
Can anybody tell me how to size the service cable from the feed through meter to two 200-amp panels at a residence. I am removing the existing CT's and meter because an addition will put the meter inside of the house. They are also going to a heat pump and removing the circuits for the electric ceiling heat for a house that is about 3000 square feet. So the load will be reduced at least 50%. The service calculates at about 140 amps max. I am planning on leaving both of the existing 200-amp panels which will be fed from this service lateral. Thanks for your help guys!
Top
2017 / 2014 NEC & Related Books and Study Guides
#165137 - 06/19/07 03:16 PM Re: Sizing of service lateral from 320 Amp meter base? [Re: homer]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Common install here (NJ) is 200 amp SEU cable (4/0 al-2 insulated, 1 bare) to each 200 amp MCB panel. Provided that panels are within acceptable distance. Option would be conduit & 4/0 al conductors.

I'm assuming that you are talking about the 'load' side of the meter, and the disconnects are in each panel?

John
_________________________
John
Top
#165150 - 06/20/07 01:28 PM Re: Sizing of service lateral from 320 Amp meter b [Re: HotLine1]
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
4/0 SEU (AL) or 2/0 SEU (CU) to each panel is the norm here in Virginia as well. We are lucky, the power company handles all final connections at the meter, so all we have to do is mount the meter socket and bring the cables into it. They do the rest.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#165187 - 06/21/07 11:30 PM Re: Sizing of service lateral from 320 Amp meter b [Re: EV607797]
homer Offline
Member
Registered: 09/30/04
Posts: 68
Loc: Vancouver, WA, USA
Thanks for your input, guys. I have a single 3" conduit, so I did some research in section 230 on service ampacity. As long as the computed load is less than the service ampacity, the cable can have a smaller ampacity than the overcurrent rating of the service. I didn't want to run parallel cables from the 320-amp meter to each panel. It looks like 350-alum will be plenty big for the two panels. It will splice in the old CT cabinet. (The CT's are going away). Thanks again for your replies!
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals