#164976 - 06/15/07 03:32 PM plug-in relay
togol Offline
Member
Registered: 09/15/05
Posts: 421
Loc: NW In. USA
my buddy "Biodiesel Man" had curbs put in at his home and somebody other than me talked him into installing ropelight in the curbs... about 400' worth of the stuff.

so I made him a little panel with the usual timer / PE and a little 8 pin relay.
the problem ???
the two ropelight circuits are a bit high.... 9A and 11A on a relay rated 10A.
I was thiking of adding a second relay and running each circuit through BOTH of the NO poles on a relay

sound stupid?

I could get a definite purpose contactor and jam it in the box ( there is a pond pump control in there too )

but I thnk the ice cubes would handle it by paralleling the feed through them.

a bit unorthodox, but it could work , right ?

_________________________
Tom
Top
Work Gear for Electricians and the Trades
#164979 - 06/15/07 05:04 PM Re: plug-in relay [Re: togol]
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
Not a good plan.

Inevitably, one set of contacts will close or open a millisecond or 2 before the other, and will erode at a much faster rate.

The best solution is a relay with properly rated contacts.
Top
#164982 - 06/15/07 05:31 PM Re: plug-in relay [Re: NJwirenut]
togol Offline
Member
Registered: 09/15/05
Posts: 421
Loc: NW In. USA
NJ, your taking all the fun out of this..;
_________________________
Tom
Top
#164984 - 06/15/07 07:00 PM Re: plug-in relay [Re: togol]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
What about just driving the coil of an A/C control relay like this one.
http://www.grainger.com/Grainger/items/6X567
You won't come close to overloading those contacts.
Joe
Top
#164986 - 06/15/07 07:32 PM Re: plug-in relay [Re: JoeTestingEngr]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Why not a solid state relay?
_________________________
Greg Fretwell
Top
#164992 - 06/15/07 10:41 PM Re: plug-in relay [Re: gfretwell]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
I thought about suggesting an SSR but a majority are 3-32 VDC control input and he doesn't need a DC supply for anything else. The AC control ones tend to be more expensive than the A/C relay that will carry more current and make sense to more people. Lastly, he can feed each string through it's own set of contacts and perhaps, separate fusing.

Greg, I knew that you would think of using an SSR just like I did. What I didn't know is if you are always reminded of SSRs in the bottom of Cartridge Module Drives, used to control spindle motors. That was the first place I encountered one back when each MB weighed more than a pound.
Joe
Top
#164996 - 06/16/07 03:45 AM Re: plug-in relay [Re: togol]
walrus Offline
Member
Registered: 07/25/02
Posts: 680
Loc: Bangor Me. USA
You can get ice cubes with 20 amp rated contacts, maybe even 30 amp
Top
#164997 - 06/16/07 04:37 AM Re: plug-in relay [Re: walrus]
gibbonsseabee80 Offline
Member
Registered: 10/10/05
Posts: 40
Loc: Chesapeake, VA
I would go with gfretwell's idea. At work we have systems with relays controlling small magnetic contactors. This might prevent re-work or premature failor later on. Just a suggestion. I like square d because the coil is enclosed/hidden and quiet.
http://www.grainger.com/Grainger/items/2CF80
_________________________
Brian Gibbons
Top
#164998 - 06/16/07 04:49 AM Re: plug-in relay [Re: gibbonsseabee80]
gibbonsseabee80 Offline
Member
Registered: 10/10/05
Posts: 40
Loc: Chesapeake, VA
Sorry I meant go with JoeTestingEngr's idea. Sorry about that Joe
_________________________
Brian Gibbons
Top
#164999 - 06/16/07 06:51 AM Re: plug-in relay [Re: gibbonsseabee80]
Mountain Electrician Offline
Junior Member
Registered: 10/01/06
Posts: 31
Loc: Maine, USA
A SSR would be a good choice for this application since space is an issue. Crydom is good, AC/DC control with high amp output available. A Crydom A1225 has AC control, 25 Amp output, and costs between 30 and 40 bucks. When you install it, put heatsink compound between the relay and the metal backplate or box or it may not last long. Properly installed, a SSR is a great spacesaver.
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals