The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
gfretwell 11
sparkyinak 10
ghost307 10
Trumpy 8
Who's Online
0 registered (), 266 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#164903 - 06/13/07 06:22 PM receptacle in drop ceiling
CRW Offline
Member

Registered: 02/11/01
Posts: 160
Loc: Bethlehem, PA USA
Is there anything that prohibits a receptacle located above a suspended ceiling, into which is plugged a piece of equipment also located above the ceiling?

Top
2014 / 2011 NEC & Related Books and Study Guides
#164907 - 06/13/07 06:49 PM Re: receptacle in drop ceiling [Re: CRW]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
You can have the receptacle ... but the cord connected equipment is not allowed.