I thought I had motors figured out. After some reviewing I'm missing something.

Anyone wanna help?

All conductors are THW 75*C terminations.

25hp, 25hp, 15hp, 5hp
208V three phase
w/ non-time-delay fuse.

What is the Feeder fuse size?

This is how I think the problem is done but Its not Im missing something.

Take the largest motor FLC @ 125% = 93.5A
Get the fuse size for 93.5A = 100A
Now add that 100A with the FLC of the remianing motors.

100
74.8
46.2
+ 16.7
= 237.7A

Round down and the Feeder fuse should be 225A

Thats wrong, apparently the answer is 350A Feeder Fuse.

Help me out here I'm missing something. Thanks.


Edited by Trick440 (06/13/07 06:07 PM)
_________________________
Shake n Bake
Top
Work Gear for Electricians and the Trades
#164906 - 06/13/07 06:46 PM Re: Motor math question... Feeder Fuse. [Re: Trick440]
frenchelectrican Offline


Member
Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
Trick440 ,, there some figures that dont really ring the bell to me but one question will the largest motors will start the same time or not ??

for me this what i will do is figure each motor seperately

25 hp @ 208v = 74.6 amp [ i did not add 125% yet ]

74.6 +74.6 + 46.2 + 16.7 = 212.1 amps

now i will add extra 25% on largest motor which is 18.65 amp more so the total load is 230.75 amp then go with 175% for time delay fuse which it will say 402 amps but i can down size a little to even 400 amp but if you used the non time delay fuse the fuse size will jump up to 690 amp non delay fuse. the nondelayed fuse is sized at least 250% so that what it get ya on the figures

if more question just post it here

Merci , Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#164918 - 06/14/07 03:00 AM Re: Motor math question... Feeder Fuse. [Re: frenchelectrican]
Trick440 Offline
Member
Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
This is a text book, masters exam question. There are many more with the same result and the answer in the book is definelty showing 350a feeder fuse.

As far as the 'non time delay fuse' I think that is just thrown in there. You use that for rating motor 'branch circuits'. (short circuit, GFCI protection). I'm don't think its used in the feeder calcs. But I could be wrong.
_________________________
Shake n Bake
Top
#164920 - 06/14/07 03:14 AM Re: Motor math question... Feeder Fuse. [Re: Trick440]
Trick440 Offline
Member
Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
Heres a copy of the question page & the answer page. Question 7 is the one I posted.

Sorry its messy looking. Not sure how I got the answers the first time around... I might of just copied out of the back of the book.



_________________________
Shake n Bake
Top
#164921 - 06/14/07 03:24 AM Re: Motor math question... Feeder Fuse. [Re: Trick440]
Trick440 Offline
Member
Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
Bah... It looks like you do use the fuse.

Largest motor X 300% (non-time delay. 430.52)
=224.4A

Now add the remaining.
224.4
74.8
46.2
+16.7
= 362.1, round down and you get a 350A feeder fuse.

I tried to figure this out for an hour last night with no luck... I come back and put 15 minutes into it this morning and get it. new day new ideas I guess.
_________________________
Shake n Bake
Top
#164923 - 06/14/07 04:30 AM Re: Motor math question... Feeder Fuse. [Re: Trick440]
walrus Offline
Member
Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
3 registered (Admin, Texas_Ranger, HotLine1), 85 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 04/03/02
Posts: 6833

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals