The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 216 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#164892 - 06/13/07 03:38 PM Above Ground Pool
sprynda Offline
Junior Member

Registered: 08/16/06
Posts: 11
Loc: Cresco, pa usa
Hello to all,
I have a question concerning an above ground pool. I need to run a circuit for two different customers that have installed an above ground pool. One customer has an heater and one does not. I know that i need to run a 20 amp circuit to each to supply the pump motor and that it needs to be on a GFI. Also, if the pool is more that 20 feet away from the home, i need to install a seperate convenience outlet that is also GFI protected. My question is that does the frame of the pool need to be bonded. We have talked to 3 different inspectors and all three told us differnt things. One stated that we need to bond to the frame of the pool, One said that we need to just bond to the lug on the pump and or heater, and one said both. i can not find it in the cose book.
thanks for any help
sam

Top
2014 / 2011 NEC & Related Books and Study Guides
#164902 - 06/13/07 06:18 PM Re: Above Ground Pool [Re: sprynda]
Trick440 Offline
Member

Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
You need to bond both. The frame and the motor. Also the ladder if its metal and any other metal within 5'.
_________________________
Shake n Bake

Top
#164922 - 06/14/07 04:10 AM Re: Above Ground Pool [Re: Trick440]
sprynda Offline
Junior Member

Registered: 08/16/06
Posts: 11
Loc: Cresco, pa usa
thanks
do you know what section in the code book this is located?

Top
#164938 - 06/14/07 10:09 AM Re: Above Ground Pool [Re: sprynda]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
680.26 and in 2005 you are also bonding all paved walking surfaces within 3 feet horizontally from the water's edge. It does not specify height so if you have paving around the pool at ground level(even brick pavers) you may have to provide this grid.
The 8ga bonding grid certainly has to pick up all metal within 5' and all equipment that touches the water circulation path.
_________________________
Greg Fretwell

Top
#164945 - 06/14/07 02:56 PM Re: Above Ground Pool [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Out of curiousity, you guys in PA....does your areas require any permits for your work?

Article 680 covers pools, and as Greg said 680.26 (2005) for bonding.

As to the receptacles:
AG pool filter, 120 volt, 20 amp twistlock, w/bubble cover no more than 3' from filter motor. (Filters have factory 3' cord w/twistlock cap) Circuit requires GFI protection; CB or deadfront device. You need a general purpose GFI no closer than 10' and no further than 20' from pool.
Bond is #8 solid (bare or green); all metal objects within 5' of pool edge, including heater, filter, frame, ladder, metalic deck/platform, fence, etc.

John
_________________________
John

Top
#165118 - 06/18/07 06:08 PM Re: Above Ground Pool [Re: HotLine1]
sprynda Offline
Junior Member

Registered: 08/16/06
Posts: 11
Loc: Cresco, pa usa
Thanks so much for all the info. It is so confusing when you get three different inspectors telling you three different things. There is alot of cunfusion between an in ground pool and an above ground pool. I was told today that i need to bond at 5 different point around the pool. My question is how do i bond to the pool. I am afraid of drilling into the frame and damagaing the pool or voiding the customers warrentee. As per us guys in PA, i guess it would depend on the town or township you live in. every town is differernt. in my case the owner did not get a permit.
thanks again for the help

Top
#165136 - 06/19/07 03:09 PM Re: Above Ground Pool [Re: sprynda]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Frame bonding is usually done by attaching a listed lug to pool hardware at either the bottom or top where the uprights attach to the rails. Not drilling holes is a real good thing. Star washers (2) on the lug where you attach it.

As to the opinions of the different AHJ's..
the best suggestion I can offer is politely asking 'what Article are you quoting (Sir)'

As to the 'PA way'...I'm aware that the Commonwealth has recently licensed Electrical Inspectors, so on that info I'm assuming that permits are required? Perhaps, not statewide yet?

John
_________________________
John

Top
#165247 - 06/23/07 07:03 PM Re: Above Ground Pool [Re: HotLine1]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I think it would be wise to find out if the pool needs any bonding at all by asking if it is by definition, a permanently installed pool or a storeable pool. If it is the later there are no bonding requirements.
_________________________
George Little

Top
#165251 - 06/23/07 08:52 PM Re: Above Ground Pool [Re: George Little]
fullyenergized Offline
Junior Member

Registered: 10/11/06
Posts: 2
Loc: PA
Quote:As to the 'PA way'...I'm aware that the Commonwealth has recently licensed Electrical Inspectors,

Thats funny.I have pictures of a job that a licensed Electrical Inspector passed that had four code violations in a new home.I have also seen other jobs where he pass other stuff that should have failed.

Top
#165283 - 06/24/07 09:56 PM Re: Above Ground Pool [Re: fullyenergized]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
There is another way to solve the storable vs permanent pool question in a more practical way. What kind of equipment are they using? Storable pool equipment is not the same as permanent equipment and they are mutually exclusive in their labelling. You can't use one on the other. If they say this is a storable pool, want bonding relief and still use permanent equipment there is your violation.
Storable equipment is usually low voltage, always double insulated and has a 25' attachment cord with a cap on it.
Storable pools are usually all plastic and most inflate.