The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 21
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 60 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#164588 - 06/06/07 05:07 PM Loomex Bundling
dougwells Offline


Member

Registered: 05/03/03
Posts: 1230
Loc: kamloops BC Canada
I may have a job cleaning up work after a homeowners permit was canceled by the safety authority.
this is what i saw in the Basement.
1 8/3... 1 14/3....2 14/2 in a one inch hole.There is also minor jacket damage.

another hole theres 1 8/3 1 14/3 and 1 14/2 in a one inch hole.
the reason i ask is i would never do this as i use many holes anyhow will this be a code correction. Thanks

Top
2017 / 2014 NEC & Related Books and Study Guides
#164597 - 06/06/07 06:58 PM Re: Loomex Bundling [Re: dougwells]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
4-004(10) permits bundling but not beyond 60mm without derating. There is the obvious repair with the damaged cable sheath, but if you can run it through the hole without damage to the cable, it is acceptable, if not always abvisable.

Top
#164598 - 06/06/07 06:59 PM Re: Loomex Bundling [Re: jay8]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
whoops, thats 600 mm without derating, not 60 mm.

Top
#164623 - 06/07/07 09:56 AM Re: Loomex Bundling [Re: jay8]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
In order to get the 80% on the wires I generally say 2X3 wire or 3X2 wire run together. No 100% rated breakers or 3 current carrying conductors max run together.
The hole should be big enough to allow all the conductors to run freely. I stop short of asking for max 40% fill of the hole diameter but it is still a good ideal to allow for holes big enough to easily allow the addition of another cable or two.
No derating on communications cables but they can stuff too many cables in a hole too.

Top