#164511 - 06/04/07 07:44 PM Conduit Body Splice
Cinner Offline
Member
Registered: 12/01/04
Posts: 78
Loc: Kelowna, B.C., Canada
Can a splice be made in a conduit body for example an LB?
Top
Tools for Electricians:
#164517 - 06/04/07 10:52 PM Re: Conduit Body Splice [Re: Cinner]
dougwells Offline


Member
Registered: 05/03/03
Posts: 1137
Loc: kamloops BC Canada
No. But I cant reference a code section They cannot be used for a junction box.
Top
#164526 - 06/05/07 05:44 AM Re: Conduit Body Splice [Re: dougwells]
ghost307 Online   content
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
314.5

There's a VERY limited exception in 314.16C2 that allows it.
_________________________
Ghost307
Top
#164532 - 06/05/07 08:32 AM Re: Conduit Body Splice [Re: ghost307]
dougwells Offline


Member
Registered: 05/03/03
Posts: 1137
Loc: kamloops BC Canada
Now we need a Canadian Code reference
Top
#164533 - 06/05/07 08:59 AM Re: Conduit Body Splice [Re: dougwells]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Some conduit bodies are approved for splices. space and wire count is very limited. The body has to have a cubic inch capacity marked on it. There are no specific rules in the CEC that say no but there are none that say yes either. The trick here is, some bodies are approved for splices and many inspectors will respect the Approved use with some evidence suplied from the wholsale and installer.
Top
#164534 - 06/05/07 04:47 PM Re: Conduit Body Splice [Re: mikesh]
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Take note that 314.16(C)(2) not only allows splices in condulets that are marked, it also allows devices to be installed in them.



Roger
Top
#164535 - 06/05/07 05:11 PM Re: Conduit Body Splice [Re: Cinner]
CRM Offline
Member
Registered: 02/29/04
Posts: 74
Loc: Alberta Canada
According the Alberta Standata Code you can't. The code does not permit "conduit fittings" to be used as a junction box. However, in Alberta we have interpreted the term "equivalent device" in rule 12-3000(1) to include "conduit fittings" in special applications (i.e. connection to solenoids, photocells, etc) Wire leads from these devices must be integral to the device. Where the device has a bonding conductor and the conduit fitting has no provisions for attaching a bonding conductor, a separate bonding conductor must be provided in the conduit system to the fitting. The fitting must also comply with the requirements of rule 12-3034 and table 22.
Top
#164542 - 06/05/07 07:00 PM Re: Conduit Body Splice [Re: Cinner]
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I would look at 12-910, and if the fitting is part of the raceway where conductors continue through then I would say no splices because the fitting is part of the raceway. But if the conduit stops at the LB, then you may have a case for splicing with sufficient space as per Mikesh's post.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 74 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals