The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 97 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#164511 - 06/04/07 07:44 PM Conduit Body Splice
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
Can a splice be made in a conduit body for example an LB?

Top
2014 / 2011 NEC & Related Books and Study Guides
#164517 - 06/04/07 10:52 PM Re: Conduit Body Splice [Re: Cinner]
dougwells Offline

Member

Registered: 05/03/03
Posts: 1228
Loc: kamloops BC Canada
No. But I cant reference a code section They cannot be used for a junction box.

Top
#164526 - 06/05/07 05:44 AM Re: Conduit Body Splice [Re: dougwells]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
314.5

There's a VERY limited exception in 314.16C2 that allows it.
_________________________
Ghost307

Top
#164532 - 06/05/07 08:32 AM Re: Conduit Body Splice [Re: ghost307]
dougwells Offline

Member

Registered: 05/03/03
Posts: 1228
Loc: kamloops BC Canada
Now we need a Canadian Code reference

Top
#164533 - 06/05/07 08:59 AM Re: Conduit Body Splice [Re: dougwells]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Some conduit bodies are approved for splices. space and wire count is very limited. The body has to have a cubic inch capacity marked on it. There are no specific rules in the CEC that say no but there are none that say yes either. The trick here is, some bodies are approved for splices and many inspectors will respect the Approved use with some evidence suplied from the wholsale and installer.

Top
#164534 - 06/05/07 04:47 PM Re: Conduit Body Splice [Re: mikesh]
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Take note that 314.16(C)(2) not only allows splices in condulets that are marked, it also allows devices to be installed in them.



Roger

Top
#164535 - 06/05/07 05:11 PM Re: Conduit Body Splice [Re: Cinner]
CRM Offline
Member

Registered: 02/29/04
Posts: 73
Loc: Alberta Canada
According the Alberta Standata Code you can't. The code does not permit "conduit fittings" to be used as a junction box. However, in Alberta we have interpreted the term "equivalent device" in rule 12-3000(1) to include "conduit fittings" in special applications (i.e. connection to solenoids, photocells, etc) Wire leads from these devices must be integral to the device. Where the device has a bonding conductor and the conduit fitting has no provisions for attaching a bonding conductor, a separate bonding conductor must be provided in the conduit system to the fitting. The fitting must also comply with the requirements of rule 12-3034 and table 22.

Top
#164542 - 06/05/07 07:00 PM Re: Conduit Body Splice [Re: Cinner]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I would look at 12-910, and if the fitting is part of the raceway where conductors continue through then I would say no splices because the fitting is part of the raceway. But if the conduit stops at the LB, then you may have a case for splicing with sufficient space as per Mikesh's post.

Top