I have A customer Who has asked if I could calculate the cost per month fo her 1/2 H/P
Single phase well pump motor.This pump is currently running on a 240v 20Amp circuit.The pumpruns on average 3hrs per day.
Top
Work Gear for Electricians and the Trades
#164466 - 06/04/07 05:07 AM Re: Estimating KWH for a customer [Re: Angel_Electric]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Angel:
Pure theory math is...
746 watts per HP
746 x 1/2 = 373
373 x 3 hrs = 1119 kw = 1.2 KWHr

Now, reality check....
either clamp the feed, or use the nameplate amperage and plug those numbers in....
xx amps times 240 volts = actual wattage, times the 3 hours

Multiply the results by the KWHr fees charged by the local POCO.

John

PS: You could check into the Technical Forums here for any additional formulas you may need. Or, post away!
Welcome to ECN


Edited by HotLine1 (06/04/07 05:09 AM)
Edit Reason: Added a "PS"
_________________________
John
Top
#164469 - 06/04/07 07:35 AM Re: Estimating KWH for a customer [Re: HotLine1]
IanR Offline
Member
Registered: 12/06/04
Posts: 328
Loc: Palm Bay FL USA
If you are just estimating I would use a little more than 746w/hp. Remember you have to take into acount things like slip and motor efficiency. I have, from my experience, found that most motors are typically closer to a KW per HP.
Still, an amp clamp or some other direct measure of actual current draw is the only way you have to be close to accurate.


Edited by IanR (06/04/07 07:36 AM)
Top
#164504 - 06/04/07 04:58 PM Re: Estimating KWH for a customer [Re: IanR]
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
Originally Posted By IanR
If you are just estimating I would use a little more than 746w/hp. Remember you have to take into acount things like slip and motor efficiency. I have, from my experience, found that most motors are typically closer to a KW per HP.
Still, an amp clamp or some other direct measure of actual current draw is the only way you have to be close to accurate.

Yes but the pump will not be using the full 1/2 hp while running. The actual rate will vary as the pressure rises in the tank. Clamp on measure of the average current from low pressure to high pressure will give the best results.
Top
#164507 - 06/04/07 05:23 PM Re: Estimating KWH for a customer [Re: jdevlin]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
OK, 1 KW per HP; .5KW per 1/2 HP x 3 hrs = 1.5 KWHr.
Based on the resi rates here (NJ) .135 KWHr, we are talking a whopping amount of .20/day; $1.40 week; 6.02month$ 72.24/yr.

Clamp & average, or clamp with a 'min-max Fluke', or if it's really important....I have a clamp on KWHr recorder.

Angel....feel free to use my projected numbers, but...check your utility KWHr rates.

John
_________________________
John
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals