The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

   
Topic Options
Rate This Topic
#164429 - 06/03/07 05:35 AM MC connectors concealed in walls?
frankgi Offline
Member
Registered: 11/23/05
Posts: 11
Loc: NJ USA
A very knowledgeable co worker of mine claims to have failed a rough inspection because of an MC connector being used in a box that is to be concealed in a wall. I believe it is a JHA vio. Any thoughts?
_________________________
"Its all about the small details"
Top
Building Codes & Related References
#164430 - 06/03/07 06:09 AM Re: MC connectors concealed in walls? [Re: frankgi]
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
I would say there is a misunderstanding somewhere in the translation of the story, or a misinformed inspector.

Roger
Top
#164433 - 06/03/07 09:30 AM Re: MC connectors concealed in walls? [Re: Roger]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Is he saying the connector is concealed or the whole box(cover not accessible).
_________________________
Greg Fretwell
Top
#164435 - 06/03/07 10:42 AM Re: MC connectors concealed in walls? [Re: gfretwell]
frankgi Offline
Member
Registered: 11/23/05
Posts: 11
Loc: NJ USA
Thanks Roger and Greg for your replies.
It was a plain old side bracketed deep 1900 box with 9 ko's (3 on 3 sides with no internal clamp)used as a switch location (mud ring added) NEC 2005 Art 330 does not mention any vio about MC connectors in walls or concealed locations.
_________________________
"Its all about the small details"
Top
#164441 - 06/03/07 12:55 PM Re: MC connectors concealed in walls? [Re: frankgi]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I have heard folks claim that 90-degree MC, or flex, fittings had to be treated as an LB would be treated, and remain accessible.

Personally, I do not share this opinion. I do concede that some such fittings have little covers that make them resemble conduit bodies, but I still do not consider them to be the same as conduit bodies.

As for straight connectors .... I'm not sure it's possible to use them without concealing them. The NEC clearly allows for fishing the material ... and it's been quite a while since I saw a box with internal clamps.
Top
#164443 - 06/03/07 01:53 PM Re: MC connectors concealed in walls? [Re: renosteinke]
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I think it is confusion with the requirement that 90 degree FMC connectors stay accessible.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#164453 - 06/03/07 05:53 PM Re: MC connectors concealed in walls? [Re: iwire]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
The only reason conduit bodies need to remain accessible is so you can pull in new conductors after the walls are closed up. You don't pull new conductors in a cable.
_________________________
Greg Fretwell
Top
#164456 - 06/03/07 06:46 PM Re: MC connectors concealed in walls? [Re: gfretwell]
frankgi Offline
Member
Registered: 11/23/05
Posts: 11
Loc: NJ USA
True Greg...or no one is going to make a splice in an MC 90 connector...imagine that!
Thanks for all the replies!
_________________________
"Its all about the small details"
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 90 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 02/21/04
Posts: 1248

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals