#164362 - 06/01/07 07:13 AM Air conditioner condenser
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
We have a roof top air conditioner condenser 230 volts, 1ph, 28.9 RLA. When the unit starts a buzzing sound is heard in the conduit. There is no short circuit and the unit seems to run fine. What would cause the buzzing noise.
Top
Work Gear for Electricians and the Trades
#164364 - 06/01/07 08:20 AM Re: Air conditioner condenser [Re: Frank Cinker]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Current inrush sets up magnetic fields in the wires and you hear the wires moving in the raceways.
Top
#164398 - 06/02/07 12:38 PM Re: Air conditioner condenser [Re: mikesh]
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Would installing larger size conductors eliminate or reduce this effect?
Top
#164402 - 06/02/07 01:14 PM Re: Air conditioner condenser [Re: Frank Cinker]
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Frank:

No, but twisting or triplexing the conductors may help.

Check out THIS THREAD for some more info on the topic.
Top
#164409 - 06/02/07 02:32 PM Re: Air conditioner condenser [Re: mxslick]
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
I have witnessed the same thing in two different situations. One was in a hotel electric room. The conduit feeding the elevator would literally make a "clink- clink" sound every time it operated. I amprobed the conductors and the amperage was going from 0 to almost 100 amps.

The other time was for a large pneumatic control system air compressor. The conduit was making more of a buzzing sound every time the compressor started.

My question is: Is this bad for the conductor insulation as the conductor moves around in the conduit?
_________________________
Peter
Top
#164439 - 06/03/07 12:48 PM Re: Air conditioner condenser [Re: CTwireman]
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Peter:

Good question...my guess would be that IF there are no burrs, rough spots or separated sections at couplings, it probably would not make a huge difference in insulation wear. Couductors will expand/contract slightly during normal use so.....

But then again, has anyone encountered any failures caused by the conductors shorting out or to the conduit, where it's possible that this rattling was the primary cause?

Iwire, togol, any such experience in your areas?
Top
#164447 - 06/03/07 03:45 PM Re: Air conditioner condenser [Re: mxslick]
togol Offline
Member
Registered: 09/15/05
Posts: 421
Loc: NW In. USA
hear it all the time, maybe more with 1ph loads than 3 ph, but since conductors do vibrate with a load on them anyway, I don't concern myself with it unless the rattling is excessive
I do know that some of them have been in service for more the ten years with no problems.and I would suggest that any vibration problems show up at the terminations and not inside a pipe, unless somebody forgot to ream the ends , as you wrote

I have also seen raceways that had disintegrated long ago with the exposed wires still looped through a coupling, outside, in the weather just humming along

_________________________
Tom
Top
#164493 - 06/04/07 03:55 PM Re: Air conditioner condenser [Re: Frank Cinker]
joncon Offline
Junior Member
Registered: 02/19/07
Posts: 20
Loc: Phoenix, AZ
Quote:
Would installing larger size conductors eliminate or reduce this effect?


I say YES.


Disclaimer:

What the hell do I know.
Top
#164540 - 06/05/07 06:46 PM Re: Air conditioner condenser [Re: joncon]
wendel Offline
Member
Registered: 08/07/04
Posts: 55
You might try a hard start kit for the compressor motor. Could save a lot of time and expense.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals