#164362 - 06/01/07 07:13 AM Air conditioner condenser
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
We have a roof top air conditioner condenser 230 volts, 1ph, 28.9 RLA. When the unit starts a buzzing sound is heard in the conduit. There is no short circuit and the unit seems to run fine. What would cause the buzzing noise.
Top
Work Gear for Electricians and the Trades
#164364 - 06/01/07 08:20 AM Re: Air conditioner condenser [Re: Frank Cinker]
mikesh Offline
Member
Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Current inrush sets up magnetic fields in the wires and you hear the wires moving in the raceways.
Top
#164398 - 06/02/07 12:38 PM Re: Air conditioner condenser [Re: mikesh]
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
Would installing larger size conductors eliminate or reduce this effect?
Top
#164402 - 06/02/07 01:14 PM Re: Air conditioner condenser [Re: Frank Cinker]
mxslick Offline
Member
Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
Frank:

No, but twisting or triplexing the conductors may help.

Check out THIS THREAD for some more info on the topic.
Top
#164409 - 06/02/07 02:32 PM Re: Air conditioner condenser [Re: mxslick]
CTwireman Offline
Member
Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
I have witnessed the same thing in two different situations. One was in a hotel electric room. The conduit feeding the elevator would literally make a "clink- clink" sound every time it operated. I amprobed the conductors and the amperage was going from 0 to almost 100 amps.

The other time was for a large pneumatic control system air compressor. The conduit was making more of a buzzing sound every time the compressor started.

My question is: Is this bad for the conductor insulation as the conductor moves around in the conduit?
_________________________
Peter
Top
#164439 - 06/03/07 12:48 PM Re: Air conditioner condenser [Re: CTwireman]
mxslick Offline
Member
Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
Peter:

Good question...my guess would be that IF there are no burrs, rough spots or separated sections at couplings, it probably would not make a huge difference in insulation wear. Couductors will expand/contract slightly during normal use so.....

But then again, has anyone encountered any failures caused by the conductors shorting out or to the conduit, where it's possible that this rattling was the primary cause?

Iwire, togol, any such experience in your areas?
Top
#164447 - 06/03/07 03:45 PM Re: Air conditioner condenser [Re: mxslick]
togol Offline
Member
Registered: 09/15/05
Posts: 426
Loc: NW In. USA
hear it all the time, maybe more with 1ph loads than 3 ph, but since conductors do vibrate with a load on them anyway, I don't concern myself with it unless the rattling is excessive
I do know that some of them have been in service for more the ten years with no problems.and I would suggest that any vibration problems show up at the terminations and not inside a pipe, unless somebody forgot to ream the ends , as you wrote

I have also seen raceways that had disintegrated long ago with the exposed wires still looped through a coupling, outside, in the weather just humming along

_________________________
Tom
Top
#164493 - 06/04/07 03:55 PM Re: Air conditioner condenser [Re: Frank Cinker]
joncon Offline
Junior Member
Registered: 02/19/07
Posts: 21
Loc: Phoenix, AZ
Quote:
Would installing larger size conductors eliminate or reduce this effect?


I say YES.


Disclaimer:

What the hell do I know.
Top
#164540 - 06/05/07 06:46 PM Re: Air conditioner condenser [Re: joncon]
wendel Offline
Member
Registered: 08/07/04
Posts: 57
You might try a hard start kit for the compressor motor. Could save a lot of time and expense.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 90 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 02/21/04
Posts: 1248

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals