#164282 - 05/30/07 07:12 AM rough-in check
azelec Offline
New Member
Registered: 04/03/07
Posts: 2
Loc: arizona
HI,

I am going into a job that is a complete remodel/rewire. The house is 90% roughed. This was done by non-electricians. Right off there are box fill issues and 2 incorrect sub-panel feeders. Overall it does not seem too bad.

My question: aside from visually tracing each wire, does anyone have a procedure that they use to ensure that each box has been feed?

Thanks
Top
Work Gear for Electricians and the Trades
#164284 - 05/30/07 12:50 PM Re: rough-in check [Re: azelec]
bot540 Offline
Member
Registered: 09/14/04
Posts: 174
Loc: Vernon Hills, IL
Sounds like it could be huge headache. I hope you charged accordingly.
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Top
#164285 - 05/30/07 01:08 PM Re: rough-in check [Re: azelec]
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
Originally Posted By azelec
HI,

I am going into a job that is a complete remodel/rewire. The house is 90% roughed. This was done by non-electricians. Right off there are box fill issues and 2 incorrect sub-panel feeders. Overall it does not seem too bad.

My question: aside from visually tracing each wire, does anyone have a procedure that they use to ensure that each box has been feed?

Thanks


From past experience, we found these jobs take longer to do then a fresh new job start, I would bid it as if if nothing was there, and add a bit extra.

These jobs can take more time to complete then a new start, be very cautious when you examine the work that was done.
Top
#164288 - 05/30/07 02:42 PM Re: rough-in check [Re: LK]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Ditto with LK. "As-built" jobs, or 'second hand' jobs are time consuming, and can be a liability...IF you don't check the complete job.

Judging by your 'box fill' and sub-panel feeder situations......look real good.
John
_________________________
John
Top
#164307 - 05/30/07 06:06 PM Re: rough-in check [Re: HotLine1]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
I have had a couple of requests like that. The first one I just said sorry, my insurance company doesn't permit me to finish someone else's work. The second one I said, rip everything out then I'll go in and give you a bid to do it from scratch.

Of course I got neither job.

By the way, are you in Tucson?
Top
#164309 - 05/30/07 06:26 PM Re: rough-in check [Re: azelec]
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Originally Posted By azelec
My question: aside from visually tracing each wire, does anyone have a procedure that they use to ensure that each box has been feed?

Thanks


YES! Ring it all out... Take one large (annoy the whole neighborhood sized) doorbell and transformer. Remove all the beakers and feeds in the panel. (Especially the neutrals) Then take all the branch circuit hots and wire them to one side of the transformer, the other to the bell. And take the other side of the bell loop and connect that to all you neutrals. (If you isolate the buss, its easier if they are all connected already...) Then go to each outlet (and close the loop like a switch) by shorting hot and neutral... Close the switches and check each lighting outlet too. when you short the wires, you hear the bell ring, and you know you have a hot and neutral. If you can isolate the grounding for the panel and not in metal studs, you can do the same for grounds too. FYI you CAN NOT do this with low voltage lighting! for that you need to power them, and put a lamp in each one...

But either way, I would video the install, and make a full line diagram of the whole place before rock!
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#164322 - 05/31/07 06:57 AM Re: rough-in check [Re: e57]
azelec Offline
New Member
Registered: 04/03/07
Posts: 2
Loc: arizona
Thanks for the help e57. And for the advice from others.

BigB I am in Sedona.



Top
#164354 - 06/01/07 03:20 AM Re: rough-in check [Re: azelec]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
You might want to megger the wiring before anything gets covered up.
Top
#164384 - 06/01/07 05:44 PM Re: rough-in check [Re: electure]
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
Originally Posted By electure
You might want to megger the wiring before anything gets covered up.


Like one of these we use on old work, take over. and fire jobs.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals