The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#164250 - 05/29/07 04:21 AM Refrigeration equipment - ground fault protection
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2343
Loc: Vienna, Austria
Not wanting to do any more thread jacking on the air conditioner thread...
 Quote:
The point is as far as the NEC is concerned it does not mater what your plugging into the circuit it only matters where there receptacle is located.

It's the very same in several European countries. For example in Austria every receptacle 32A and smaller HAS to be protected by an RCD with no more than 30mA trip current. And I never heard of any problems with that, not even running 1960s vintage refrigerators. Right now we're running 2 refrigerators and an upright freezer on one RCD and had ONE inexplicable trip in over 10 years!

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#164259 - 05/29/07 10:01 AM Re: Refrigeration equipment - ground fault protection [Re: Texas_Ranger]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
It may be a matter of the setting -our GFI is set at 5mA, while the AFCI is set at 30mA- or a difference in the specific electronics of the RCD.

It's a good subject for discussion, though. At least one manufacturer of high-end built-in refrigerators for the residential market (Dacor) specifically states in its' instructions that the refrigerator needs to be on its' own NON-GFI protected circuit.

Where the problem might arise is when the refrigerator is plugged into one of the counter-top 'small appliance' circuits, which are GFI protected.

A few years back, our GFI's were re-designed; the changes are claimed to reduce nuisance tripping.

Personally, I have only encountered the problem with refrigerators that were at the end of their lives - in other words, the GFI's were working as they were supposed to!

Some of the opposition seems to be based upon a 'cost/benefit analysis." That is, the cost of losing a fridge full of food, as contrasted to the small chance of a fault.

Top
#164280 - 05/30/07 01:48 AM Re: Refrigeration equipment - ground fault protection [Re: renosteinke]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2343
Loc: Vienna, Austria
My post was mainly a reply to Trumpy's post who referred to NZ 30mA RCDs which are the same as ours in Europe.

Top
#164349 - 05/31/07 11:44 PM Re: Refrigeration equipment - ground fault protect [Re: Texas_Ranger]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Ragnar,
With respect to 30mA RCD's.
The fact of the matter is, that refrigeration equipment manufacturers, cannot reduce the leakage current from the compressor motor enough to satisfy anyone here that a fridge or other such appliance on an RCD supplied circuit.
Why this is Ragnar, is because the actual motor and the compressor unit are in a hermetically sealed unit, as in together.
Now, here is the sticking point, a Fuse or MCB will (or should) carry the in-rush current to start the system.
Now, in a sealed system, that should run forever.
But wait, what say that the system ices up because (in an A/C system) the person using it runs it too hard?.
(Expecting 30C out of a split system on a -10C morning is a bit much).
The more you work a refrigeration system the higher the leakage currents.
Usually the currents are in the Nano-amps, but once you leave a fridge or a freezer during the middle of summer, then it will trip an RCD .
Nothing annoys me more than hearing from a Home-owner, that the company that installed the fridge moved the wire over in the switchboard, "It took all our protection away!".
Idiots.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#164367 - 06/01/07 09:33 AM Re: Refrigeration equipment - ground fault protect [Re: Trumpy]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I think these are really ground faults from the internal windings in that compressor shorting out.
_________________________
Greg Fretwell

Top
#164390 - 06/02/07 01:59 AM Re: Refrigeration equipment - ground fault protect [Re: Trumpy]
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Originally Posted By: Trumpy
The fact of the matter is, that refrigeration equipment manufacturers, cannot reduce the leakage current from the compressor motor enough to satisfy anyone here that a fridge or other such appliance on an RCD supplied circuit.


Mike I don't understand what your saying.

Are you suggesting manufacturers can not reduce the leakage current?

Here in the US countless refrigerators and freezers are on 5 ma GFCI protection and are working fine.

The NEC requires this 5ma protection in a fast growing list of locations.





Edited by iwire (06/02/07 01:15 PM)
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#164405 - 06/02/07 01:23 PM Re: Refrigeration equipment - ground fault protect [Re: iwire]
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
I worked with a company that sells vending machines, both refrigerated and non-refrigerated. The older machines had so much leakage current that GFI's wouldn't hold. Even when the chilling unit was replaced they'd still trip. (The chillers are usually a separate "skid-mounted" unit so it could be readily changed out in the field.) Most replacement units had new, modern compressors.

The problem seemed to lie more in the internal wiring of the machine breaking down than any problems with the chillers. Soda machines especially would have serious issues, that soda will eat up anything! \:\)

Some machines also had bad control transformers that would have a lot of leakage current.

Bob noted:

 Quote:
The NEC requires 5ma this protection in a fast growing list of locations.


IIRC, aren't ALL vending machine installations one of those locations?

Top
#164407 - 06/02/07 02:01 PM Re: Refrigeration equipment - ground fault protect [Re: mxslick]
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Originally Posted By: mxslick
IIRC, aren't ALL vending machine installations one of those locations?


Yes that is true, new machines are supposed to have GFCI protection built into the cord but units without this are required to be supplied by a GFCI circuit.

How this is supposed to be enforced I have no idea.

I don't have my 2005 NEC handy or I would post the section that spells this out.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#164431 - 06/03/07 08:49 AM Re: Refrigeration equipment - ground fault protect [Re: iwire]
JohnJ0906 Offline
Member

Registered: 10/19/06
Posts: 65
Loc: Baltimore MD USA
 Originally Posted By: iwire
 Originally Posted By: mxslick
IIRC, aren't ALL vending machine installations one of those locations?


Yes that is true, new machines are supposed to have GFCI protection built into the cord but units without this are required to be supplied by a GFCI circuit.

How this is supposed to be enforced I have no idea.

I don't have my 2005 NEC handy or I would post the section that spells this out.


422.51 Cord and Plug connected Vending Machines

Top
#164437 - 06/03/07 12:40 PM Re: Refrigeration equipment - ground fault protect [Re: JohnJ0906]
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
Bob, John, thanks for the references!! \:\)

At least in this case my little brain isn't off track.

Top